edd_the_cat

Hi am new to the forum, am a industrial sparky with a need of some advice.

Have a problem with a lighting circuit in my flat, the circuit has 5 light fittings as well as a 12V lighting rail system in the living room. Three of the light fittings are working as required the other two and the lighting rails are not. I found one of the light pendants was a dead short across the fitting so I disconnected all but one of the light pendants, I cannot find the lighting rail transformer to disconnect it. At the Lighting rose of the pendant which I left connected, but which was not working, I got the following readings.

With no lamp in fitting.
P-N 125V
P-E 248V
N-E 55V

With lamp in fitting
P-N 59V
P-E 248V
N-E 175V which fades to 151V

I can see why the light fittings are not creating the potential across lamps which they need to function correctly, but I cannot find the fault that is supplying 55V through the neutral to earth when the lamp is out. Any help would be really greatly appreciated.
 
classic poor connection neutral or broken neutral. it will be between the last working light and the first faulty one. if you are lucky, it will be at a light. but could be a JB where someone has spurred off.
 
I would break the circuit down (when isolated of course) check continuity of conductors between the last working and first non working light just by shorting ends and checking with a multimeter see what readings you get on what cores etc
 
beaten to it. either that or use a wander lead on the neutrals. ( a length of single cable will do )
 
Where ever you think it is then it's not. It will be in the most awkward and inaccessible place going.


It may be possible they are looped through at the switches. (with a bit of luck in this case). The transformer may be hidden in a cupboard somewhere. If they are converted flats or the older ones you may have a job on your hands if they have been done from above.
 
just have to work logically. set up a work station, tool box, meter, site radio, some bits if cable, a few beers, then trace fault from a to b to beer, to fault.
 
Aye have just done a wandering lead test on my neutral, have defiantly lost my neutral between the two sides of the circuit. The neutrals are only looped through one switch. Checked for the transformer everywhere obvious but no luck I bet its tucked up in the roof somewhere, anyway thanks for the help guys, at least the fault is getting narrowed down.
 

Reply to Lighting circuit fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
690
  • Question
No live and neutral at the wall. But that would be the switch live right?
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top