Was asked to look at this job today where the lights on a 6a mcb wouldn't reset. I turned up watched the the person onsite reset the mcb where it instantly reset with a bang and arcing coming from it. I did it again, same thing happened. So i turned all the light switches off and reset the mcb and it held in so i thought great so i switched each switch on one by one expecting the circuit to blow which it didn't and it held in so turned the mcb of and on again and it held in. I then did an insulation test LN-E about 140ohms bit lower than what i was expecting as was a new circuit roughly 8 years old i'd guess. There was 2 out side fittings on this circuit so i looked in them thinking there could be some water inside after the heavy rain we've had both bone dry and no signs of damage ZS 1.04 which was what i was expecting. I Then decided that i would open up all 8 light fittings in the corridor and in every light all the ballasts seemed fine no slightly nicked cables which i could see. But i did change 2 2D lamps which where looking very black and proberly about to die. The only thing i did find wrong was that the emergency lights where wired wrong. when you turned the key switch off the switch live remained live instead of killing all power to the fittings as it should do.

i have no idea where do go from here. Maybe disconnect every fitting and do an insulation test bewteen live and neutral, but im thinking this will be clear as the mcb isn't popping. any ideas what may be happening?
 
Most probably a wet joint box, and by repeatedly resetting the mcb you've blown the fault clear.

Start by splitting the circuit down, and follow the leg with the lowest I/R reading.
 

Reply to lighting circuit inconsistent tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
659
  • Question
As said, looked like there was enough cable slack to correct direct and avoid fitting the wagos in ceiling void
2
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top