I went to a customer this afternoon to look at downstairs lighting circuit which was not working. It's a 4 way wylex board with a resettable 5amp breaker for the lighting circuit. This was off and would not reset. Apparently the fault occurred a few days ago when owner switched on light and nothing happened, no bang, just not working.
They had a new boiler fitted two weeks ago. Most work was done in former airing cupboard upstairs, and in loft area accessed from bathroom, which is adjacent to boiler cupboard. It was just a new boiler with wireless controller.
I removed all loads and did IR readings and got 0.00MOhms between line-neutral, line-earth,neutral-earth. Did continuity test between line-neutral and got just under 4 ohms - presumably the resistance of the circuit that was short circuited at some point.
I've checked all pendants and other light fittings including some dodgy looking wall lights, and disconnected them one by one but IR readings stayed the same.
I put my head up in the loft area where some new pipes have been run to see if i could see any damage to cables and saw lots of fairly recent looking droppings - I think they were too big for mice, so probably rats. the house owner said they had had rats a couple of years ago, but had got rid of them and hadn't heard any scurrying of feet recently, whereas that was what alerted them before. as their house is now nice and warm with the new boiler they wondered if that might have attracted rats back.
I've left it with them for now and they are calling in a rodent control company before I do any more work.
I've not come across rodent damage to cables before although I've read about it on here. From your experience do you think this is a likely cause of the problem? When I go back is it a case of just visually inspecting the cables to look for damage?
Thanks for any help.
I went to a customer this afternoon to look at downstairs lighting circuit which was not working. It's a 4 way wylex board with a resettable 5amp breaker for the lighting circuit. This was off and would not reset. Apparently the fault occurred a few days ago when owner switched on light and nothing happened, no bang, just not working.
They had a new boiler fitted two weeks ago. Most work was done in former airing cupboard upstairs, and in loft area accessed from bathroom, which is adjacent to boiler cupboard. It was just a new boiler with wireless controller.
I removed all loads and did IR readings and got 0.00MOhms between line-neutral, line-earth,neutral-earth. Did continuity test between line-neutral and got just under 4 ohms - presumably the resistance of the circuit that was short circuited at some point.
I've checked all pendants and other light fittings including some dodgy looking wall lights, and disconnected them one by one but IR readings stayed the same.
I put my head up in the loft area where some new pipes have been run to see if i could see any damage to cables and saw lots of fairly recent looking droppings - I think they were too big for mice, so probably rats. the house owner said they had had rats a couple of years ago, but had got rid of them and hadn't heard any scurrying of feet recently, whereas that was what alerted them before. as their house is now nice and warm with the new boiler they wondered if that might have attracted rats back.
I've left it with them for now and they are calling in a rodent control company before I do any more work.
I've not come across rodent damage to cables before although I've read about it on here. From your experience do you think this is a likely cause of the problem? When I go back is it a case of just visually inspecting the cables to look for damage?
Thanks for any help.