glasgospark

upgraded board to dual rcd
everything ok
that night lighting circuit breaker trips rcd stays on
i go back try putting breaker back on trips after a couple minutes , every light in house working when breaker on
tried disconnecting all outside lights etc, also still tripped with every light switch in off position ,
after numerous attempts trying different things the rcd then tripped along with the mcb , now rcd wont stay on when lighting mcb is on everything else in house is ok , i have tried a different mcb for lighting and still happens , it also stayed on for 4 hours yesterday untill ittripped that night ,

no timers on circuit or anything

any thoughts
 
so, do the same on continuity, get an idea of the resisiance. then start opening fittings and switches. could be a trapped cable or a screw into a cable.
 
Get the IR meter on the case check no issues, are all neutrals in the correct order?
I had a similar issue once turned out to be a damaged cable below a floor board IR was >5 meg but when someone stood on the floor board it caught the nail below lucky find in the end,
I would love to meet the plumber who caused it
 
Get the IR meter on the case check no issues, are all neutrals in the correct order?
I had a similar issue once turned out to be a damaged cable below a floor board IR was >5 meg but when someone stood on the floor board it caught the nail below lucky find in the end,
I would love to meet the plumber who caused it
Funny you should mention that , when it was just the McB tripping 2 times in a row at a squeaky floorboard when stood on it tripped straight away but after that nothing now it's rcd , which made me think its worked its way through the neutral cable now causing Imbalance on circuit and not a dead short ,
 
If the MCB trips after a few minutes it is either carrying about twice the rated current or something is heating up and then causing a fault. Clamp test the circuit of it can stay on and check the load.

Once this fault has occurred several times the expanding damage has now involved the cpc and caused the RCD to trip.

Split the circuit and IR test the sections until you can narrow down the location.
 
If the MCB trips after a few minutes it is either carrying about twice the rated current or something is heating up and then causing a fault. Clamp test the circuit of it can stay on and check the load.

Once this fault has occurred several times the expanding damage has now involved the cpc and caused the RCD to trip.

Split the circuit and IR test the sections until you can narrow down the location.
It's only pulling 2.8amp full load , I took earth out the circuit also and it stayed on for 4 hours then tripped , of course not a solution but I was testing the waters
 
If the MCB tripped and the RCD stayed on then initially you had a L-N fault so as advised check the whole circuit because I think you have agrivated the situation when you were switching the MCB on.

Also what was the point of this did you hope the fault would go away ?
 

Reply to lighting circuit problems in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
347
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top