Mwoods4757

Hi all I'm trying to get my head around contactors. I understand how they work and what they are just finding the wiring a little hard

I know the
coils are on a1 and a2 which is the control circuit.
So do you have the supply coming in to the top terminals and the load to the light going out from the bottom and you just link from a1 and a2 to the overload?
Is there always a overload too.

Any information would be appreciated or simple diagrams if possible.
 
you would not generally use an overload except on motors. think of a contactor as a relay. you apply the control voltage to A1/A2 and the contactor pulls in L1-T1, L2-T2, L3 -T3.
 
Cheers all. So the control circuit on the coils a1 and a2 is this where your ssupply would be?

Also would you need to link out the terminals at the top to the load on the bottom?
 
Cheers all. So the control circuit on the coils a1 and a2 is this where your ssupply would be?

Also would you need to link out the terminals at the top to the load on the bottom?

If your switching and load are coming from the same supply / cct, then yes. If fior example you were in a 3ph environment and had three banks of lights, one on each phase, then you'd be using a 3 pole (or probably 4p with the neutral) contactor, so you'd have:
Ph 1 - L1
Ph 2 - L2
Ph 3 - L3
N - N

but then you'd need to be using one of the phases as your switch cct, so you might have :

Ph 1 - A1
Ph 1 - L1
etc.

Or in a single phase environment then yes you would gang all the L's to the A1 feed. Depending on the type of contactor sometimes you can even use a bit of busbar.
 
Your contractor basically breaking the load of your chosen circuit.this circuit is opened/closed by a switch,photocell,time clock,PIR etc.a1 is your switch wire a2 is your neutral.On the contractor depending on make or model it will have for a 4 pole one 1,3,5,7 on the top and 2,4,6,8 on the bottom your permanent feed side goes into 1,3,5,7 and the switched side into 2,4,6,8.
 
Never use a four pole for 3ph lighting. The neutral isn’t late break, so you run the risk of a momentary floating neutral and all the problems that can cause.
 

Reply to Lighting contactors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
560
  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top