Ok this is a pretty basic question but can someone please refresh my memory

If I have a circuit with lets say 3 points

From DB to first point to second to third

As an example lets say that each point draws 5 a of current each

Will the cable from DB to point 1 be carrying 15A,
The cable from 1 to 2 carrying 10A
The cable from 2 to 3 carrying 5A

under full load

Is this correct?
 
depends on the size of the cable and the MCB in the CU

I think the 15A was meant as an example of 3 points pulling 5A each, not necessarily a lighting circuit.

The first length of cable would be carrying 15A as that would be feeding all 3 points.

The second length of cable would carry 10A as that would be feeding the last 2 points only.

The last length of cable would only be feeding the last point, so would only be carrying 5A.
 
I think the 15A was meant as an example of 3 points pulling 5A each, not necessarily a lighting circuit.

The first length of cable would be carrying 15A as that would be feeding all 3 points.

The second length of cable would carry 10A as that would be feeding the last 2 points only.

The last length of cable would only be feeding the last point, so would only be carrying 5A.

Post #3 states downlighter.

Theres another post by the same individual asking another similar question.
 

Reply to Lighting Current in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
204
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
559
Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...
Replies
6
Views
732

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top