To note here you say its less than 6months old if it is found to be the fault of another trade and through no installation issues with the electrics then they may be liable to all costs but you should notify them before doing the works .... but if the customer isnt aware of this it sometimes isnt worth all the hassle that comes with going down this avenue .....tell her to get her spare wallpaper roll out and chop the bugger out
The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.
This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.
You mention “best codes of practice” and then suggest flying in the face of one of the most fundamental safety systems in the book.
Make the lighting circuit PME and be done with it! At least a short to the CPC from the live would bring out the MCB!
I’m sorry (not) you find my first reply abrupt and offensive (it was meant to be). Don’t expect me (or anyone else) to condone your creation of what could become a fatal scenario!
Disconnect faulty/damaged cable run new, there must be a way from getting to the cu to the first light, run cable in back of fitted cupboard or some where
The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.
This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.
Well if the ESC say it's fine, I might wire my next lighting circuit in singles and miss the CPC out then. If something goes badly wrong I can stand in front of the judge and try that as my defence.
As you state Silentboarder this is supposed to be a professional forum, maybe that's why your preposterous suggestion is being shouted down.
The ESC advice on lack of CPC's on lighting circuits is not intended for a scenario the OP finds himself in......nowhere does it state a lighting circuit 'is fine to be wired without a CPC'...!
The guide is intended to cover a CU change where the client refuses rewiring of a circuit which does not meet current standards,but can be left in a safer state than it was before by following the best practice guide....it's not intended to bodge a fault so that it doesnt trip an RCD.
Yes the ESC do say you can wire in a circuit without a cpc this is normally when the cable hasnt got a cpc , you have a fault on the cable which could be a nail through the cable which could be arcing across the inside of the cable which is a potential fire hazard , take a continuity measurement on the cable you could then get a approximate idea where the fault is and rectify it or find an alternative route