silentboarder69

Hi,
I was called to a customers house as their RCD keeps tripping. I isolated the faulty circuit and began testing.
The fault unfortunately is on the feed from the CU to the 1st floor lighting circuit, and between the neutral and CPC.
I know from installing CUs, that if a lighting circuit has no CPC, you can still install a new CU as long as the resistance between R1/Rn and the earth terminal is > 1MOhm, you can install the new CU (ESC Best Practice Guide 6).
The customer has just had their house refitted, and it wouldn't be ideal to replace the faulty cable.

Would it be safe to reconnect the circuit without connecting the CPC? It is RCD protected. Assuming it meets the tests outlined in ESC Best Practice Guide?
If it is OK, would there be any point in connecting the CPC to the CPC on the 32A circuit?

I'm just exploring these options...
 
No....not acceptable IMO. The cable is clearly damaged,and if you remove the cpc you cant justify by the fact that there's an RCD protecting because without an earth fault path the RCD is redundant as a means of disconnection if the fault 'develops'......a way to rewire the affected cable or otherwise clear the fault has to be found.
 
Not really IMO. What has caused the fault?

No idea. The installation is approx six months old. The CU is in the cellar, and the first point is on the first floor. There is nothing obvious, so anything I say would be a pure guess. There doesn't seem to be any defects in the walls, or new work that has been carried out since the installation. I could only guess at rodent damage?
 
would it be easy to connect the the first point of the lighting circuit to the nearest other CPC on the first floor? i have no idea if this is acceptable or not, just a thought
 
No idea. The installation is approx six months old. The CU is in the cellar, and the first point is on the first floor. There is nothing obvious, so anything I say would be a pure guess. There doesn't seem to be any defects in the walls, or new work that has been carried out since the installation. I could only guess at rodent damage?
Carpets, plumbing, things screwed into the ceilings etc etc etc???

If all the points are in good order then it's break the circuit into legs and test until you find the culprit. If it's a damaged cable then it needs replacing.
 
It is fairly uncommon but I have known the neutral to be moulded into the earth in T+E direct from the factory, only showed up under load. Whatever your problem is though, disconnecting the earth is not an option, all circuits have required a cpc since (quite a long time, well before my time) and think if you were to remove the earth and leave it in the cables (i.e. cut off the ends) any further faults e.g. screws through cable, would not be detected but could lead to a nasty belt from the un-earthed cpc.

Find the fault and repair it is the only option!
Good luck!
 
as above posts.bite the bullet and replace the damaged section. maybe you can find a route up in cupboards.
 
I can’t believe you even considered disconnecting the earth, never mind coming on here asking if it’s OK.

First and foremost it would be downright dangerous as others have explained.
 
Not sure how many lights your talking about, and if theres other lighting circuits.(would be best if there is) But what about disconecting the damaged leg completley and Refeeding any of the affected lights via a fused spur off a socket.
not ideal and rewireing the faulty leg would be best but sometimes needs must...
 
The fault is what it is if it needs replacing thus effecting the deco then that be the case.... yes take your customers wishes into account but dont let the cart lead the horse here, communication is just as much a skill as been competent so break the lighting circuit down into sections, find the offending section and further break it down until you have located the fault to one leg or joint in the cable then tell the customer what is required and the options be careful they dont dictate to you but be aware of their concerns.
NO! its not acceptable to piggy back the earth onto another circuit, final circuit earthing must be seperate in your particular case, just for reference it is permitted to use 1 earth for multiple circuits if say your using a trunking or conduit as the earthing with more than one circuit contained within, in you idea all it would take is for someone to disconnect the earth of another circuit to effectively leave the lighting without earthing whether this be for testing purposes or alterations by a future electrician.

Check also that outside lighting isnt the issue here with water ingress, ask if any recent works have been done be it pro' or DIY of any type, get as much info as possible, the number of times in my early days ive located a fault and the customer has then said Oh yes we just had someone in working on or fitting that.... now i know exactly what to ask to minimise my time and effort and keep the customer smiling....in most cases!
 
Last edited by a moderator:
The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.

This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.
 
I can’t believe you even considered disconnecting the earth, never mind coming on here asking if it’s OK.

First and foremost it would be downright dangerous as others have explained.


The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.

This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.
 
The fault is what it is if it needs replacing thus effecting the deco then that be the case.... yes take your customers wishes into account but dont let the cart lead the horse here, communication is just as much a skill as been competent so break the lighting circuit down into sections, find the offending section and further break it down until you have located the fault to one leg or joint in the cable then tell the customer what is required and the options be careful they dont dictate to you but be aware of their concerns.
NO! its not acceptable to piggy back the earth onto another circuit, final circuit earthing must be seperate in your particular case, just for reference it is permitted to use 1 earth for multiple circuits if say your using a trunking or conduit as the earthing with more than one circuit contained within, in you idea all it would take is for someone to disconnect the earth of another circuit to effectively leave the lighting without earthing whether this be for testing purposes or alterations by a future electrician.

Check also that outside lighting isnt the issue here with water ingress, ask if any recent works have been done be it pro' or DIY of any type, get as much info as possible, the number of times in my early days ive located a fault and the customer has then said Oh yes we just had someone in working on or fitting that.... now i know exactly what to ask to minimise my time and effort and keep the customer smiling....in most cases!


Thanks mate, that makes perfect sense re the CPC connecting to another circuit.

Re the fault, I have located it, but it's the worst kind, a fault in a cable burried in the wall. My first line of advice was to replace the faulty cable, but just want to be double sure I'm not creating work when there may be a better option. A fused spur off the 32A may be a good alternative that I hadn't thought of.

All the best.
 
The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.

This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.

Who are you directing this at? My post IMHO is both helpful and informative, having no earth in a lighting circuit can be acceptable but usually steps have to be taken, clearly identified at the board all fixtures and fittings are class 2 etc etc ... you case is you are going into an existing circuit which has an earth, therefore you cannot leave it without an earth to satisfy clearing a fault as you would be leaving it less safe than you originally found it.

Edit..... soz was typing before you posted last so ignore the first bit of this.
 
To note here you say its less than 6months old if it is found to be the fault of another trade and through no installation issues with the electrics then they may be liable to all costs but you should notify them before doing the works .... but if the customer isnt aware of this it sometimes isnt worth all the hassle that comes with going down this avenue .....tell her to get her spare wallpaper roll out and chop the bugger out :)
 
or alternatively, diss. the faulty section and replace with new cable taking a different route that is less disruptive to the decor.
 
The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.

This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.

You mention “best codes of practice” and then suggest flying in the face of one of the most fundamental safety systems in the book.

Make the lighting circuit PME and be done with it! At least a short to the CPC from the live would bring out the MCB!

I’m sorry (not) you find my first reply abrupt and offensive (it was meant to be). Don’t expect me (or anyone else) to condone your creation of what could become a fatal scenario!
 
Last edited by a moderator:
The Electrical Safety Council say it's fine to wire up a lighting circuit with no CPC, why don't you send your poorly thought out email to them as that's where I got my info, and I would suggest they know more than you.

This is supposed to be a professional forum, not a childs forum for slagging people off. I suggest you find an alternative forum if this is what you wish to do.
Well if the ESC say it's fine, I might wire my next lighting circuit in singles and miss the CPC out then. If something goes badly wrong I can stand in front of the judge and try that as my defence.
As you state Silentboarder this is supposed to be a professional forum, maybe that's why your preposterous suggestion is being shouted down.
 
Have another read of the ESC guidence note and then ask the question again.

I think you will find the CPC issue revolves around CU changes only and not installing new circuits without CPC's.

I will mention this post on Thursday when I speak with them at Coventry !
 
The ESC advice on lack of CPC's on lighting circuits is not intended for a scenario the OP finds himself in......nowhere does it state a lighting circuit 'is fine to be wired without a CPC'...!
The guide is intended to cover a CU change where the client refuses rewiring of a circuit which does not meet current standards,but can be left in a safer state than it was before by following the best practice guide....it's not intended to bodge a fault so that it doesnt trip an RCD.

Edit....wot tonymc said but he types quicker!
 
Why not just bypass the RCD?

Who needs them anyway?

Infact cut all the cpcs out and bypass the RCD that will defo fix the problem, no nuiscence tripping ever again?

If there are problems with it in the future pop a 63A MCB on the circuit
 
Is this a job that was posted on Rated People in Bristol today by any chance?

;)

:thumbsup
 
Yes the ESC do say you can wire in a circuit without a cpc this is normally when the cable hasnt got a cpc , you have a fault on the cable which could be a nail through the cable which could be arcing across the inside of the cable which is a potential fire hazard , take a continuity measurement on the cable you could then get a approximate idea where the fault is and rectify it or find an alternative route
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Lighting Fault, Earth to Neutral Tripping RCD
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
silentboarder69,
Last reply from
nickblake,
Replies
27
Views
10,527

Advert

Back
Top