Evening all. Your thoughts please:
I was helping out another spark today. The job was to spur from a ring final to a 13A fused spur, to feed several sockets and some lighting in a loft conversion. For the lights (regular common or garden pendant sets) he asked me to fuse down further to 3A, via another fused spur. It's his job so I did it, but I wonder if the 3A fused spur was really necessary?
The relevant reg seems to be 559.5.1.204:
Lighting circuits incorporating B15, B22, El4, E27 or E40 Lampholders shall be protected by an overcurrent protective device of maximum rating 16 A. To me, this is achieved by the 13A BS1362 fuse, but perhaps there's something I'm missing.
I was helping out another spark today. The job was to spur from a ring final to a 13A fused spur, to feed several sockets and some lighting in a loft conversion. For the lights (regular common or garden pendant sets) he asked me to fuse down further to 3A, via another fused spur. It's his job so I did it, but I wonder if the 3A fused spur was really necessary?