Clients bought some track lighting(catenary wire type with anchors etc) to install in three bedrooms upstairs. All rooms are on the same B6 MCB. Each comes with 4 lights to screw on to the 12v wire track.
Transformer is 210VA 230v-12v step down
Calcs-
230v/210VA = 1.1A per track setup, 4x50w halogens will be fine per setup.
The transformer is rated at 15A and has an inline fuse protecting it. I am assuming the transformer isnt actually pulling 15A continuously its just a protective measure?
Lastly the transformer keeps tripping the mcb if switched on and off in succession, i think this down to inrush current and will be upgrading to a D6 MCB. Can anyone confirm my calcs and my theory on the 15A scenerio.
Cheers Lanky