Clients bought some track lighting(catenary wire type with anchors etc) to install in three bedrooms upstairs. All rooms are on the same B6 MCB. Each comes with 4 lights to screw on to the 12v wire track.

Transformer is 210VA 230v-12v step down

Calcs-
230v/210VA = 1.1A per track setup, 4x50w halogens will be fine per setup.

The transformer is rated at 15A and has an inline fuse protecting it. I am assuming the transformer isnt actually pulling 15A continuously its just a protective measure?

Lastly the transformer keeps tripping the mcb if switched on and off in succession, i think this down to inrush current and will be upgrading to a D6 MCB. Can anyone confirm my calcs and my theory on the 15A scenerio.

Cheers Lanky
 
zs comes in at 1.45, C6 would still be too sensitive if all three are turned on (kids bedroom). doesn't help with the fact they're are loads of halogens on the same circuit.
 
zs comes in at 1.45, C6 would still be too sensitive if all three are turned on (kids bedroom). doesn't help with the fact they're are loads of halogens on the same circuit.

The transformers will have high start up currents so unless they are switched on at exactly the same time.

What size is the cable?
 
You can't tell the exact running current because you don't know the power factor but fully loaded it would be > 210/230=0.9A (not sure why you wrote 230/210 but 1.1-1.3A is not a bad estimate allowing for pf). The 15A internal breaker is on the output side - with 200W on 12V the output current is 200/12= 16.6A but they will be partially using up the fusing factor of the MCB.

The inrush on these is notoriously high. A C6 might hold, IIRC I had some on C6's and some on C10s in our old offices. Problem I had was too many transformers on each switch, IIRC I replaced some of them with alternative types with lower inrush.
 
Its the scenario where looks come before practicality sadly, id rather use a more effective electronic transformer but these are not decorative. I would have used LED's throughout but clients adamant. Thanks for the help lads appreciated, C6 it is.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Lighting transformer help!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
LankyWill,
Last reply from
LankyWill,
Replies
8
Views
781

Advert

Back
Top