lighting | on ElectriciansForums
Discuss lighting in the Australia area at ElectriciansForums.net
P
peteludman
just a stupid question my brain is a mess at moment.
i want to fit another 10 fluresent lights high frequency on top of 10 of the same lights so 20 all together the tubes are 26 w 1 tube in each.
i get 2.2A for the lot so a 10A breaker would be fine and switch would be fine to.
is this the right way of working it out, looking at the tube wattage i know there would be a start up current but a type c breaker would take that wouldnt it
just let me know if im wrong or right and just being stupid
thanks:cool:
when calculating current for cable calculations or switch gear etc for fluorescent lights i think it is usual to multiply by a loading factor of 1.8.
So even a type B, 6A mcb should be ok - a 10 A mcb would still be fine for protecting 1.5mm cable if the installation method is nothing out of the ordinary.
Reply to lighting in the Australia area at ElectriciansForums.net
By the looks of it the whole head comes off in one unit, guess it has a driver inside of it. Ive tried to Google the Image i have, one comes up...
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...