J

jimmycomeruk

I am currently installing earth rods as lightning protection for shared satellite dish tv systems on blocks of flats.

My query is do I have to install an earth rod for lightning protection or can I earth to the electrical supply?

I'm pretty sure I should be able to earth to the supply but confirmation would be much appreciated.
 
hi
542.4.1
in every installation a main earthing terminal shall be provided to connect the following to
(iv)
lightning protection system bonding conductor

This is not the OP's query...the quote above concerns main bonding of lightning conductors ,NOT earthing.
Main bonding of lightning conductors should only be undertaken after consulting a specialist.
Regarding the op I would suggest this is a specialist area and if you dont know what you are doing you shouldnt be doing it.
 
definitely agree - i wouldn't go near it

it's a highly specialized field

i'm still trying to picture you installing these rods-how are you doing it

hope you're using bigger than 2.5?:D
 
Regarding the op I would suggest this is a specialist area and if you dont know what you are doing you shouldnt be doing it.

I know what I am doing and the method I am using is correct. HOWEVER on occassions the perimeter of some buildings do not have anywhere to install an earth rod and I wanted confirmation of whether I could use the MET of the buildings as lightning protection. I am using rods 16.5mm and 2m length. I test for continuity from the dish to the rod then peform a soil resistivity test.
 
I think you would have to ask the DNO.... But I guarantee a big fat NO...

Bonding lightning conductors is just to ensure that should a mains voltage appear on the conductor, it is safely conducted to earth ad the overcurrent protective device operates. It is definitely not to send lightning type current back to the centre point of the transformer that's for sure.

Besides, lighting has no interest in the centre point of the transformer; it just wants the fastest route to earth....
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Lightning Protection Earthing Method?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
jimmycomeruk,
Last reply from
GStueyXR,
Replies
10
Views
5,953

Advert

Back
Top