There's always been conflictions of interest with testing lightning conductors since the regime of testing was put onto the electricians back in 81/83.
When I last did a job like the one your on, it was the same set up with power, and 5 submains on different parts of the building. I just ran a 25 mm bond to the conductor and labelled it, then connected it to the split earth bar. The niccy inspector just asked me my method of testing for continuity of the bond?
I told him as I had installed it, I didn't bother testing it along with the other bonds, I just worked out its resistance according to its length, I had a wander lead with me (an 100 m shagged roll of 2.5 single on a wooden reel) and he asked me to test it. And it was < 0.05 ohms just as I had recorded it on the EIC. When I asked him just out of interest if the electrode would've have been suitable for a TT, he said no as it would've had dual functionality?