Hi,

I have been called back to a job where a 3-halogen lamp fitting with 2 way switching keeps blowing a bulb. When this happens and the switch is turned off the remaining 2 lamps stay on but very dim. When the blown lamp is replaced, all is well again. I have tried everything. Isolated it from upstream lights, changed both double switches and tightened all terminals. Any ideas? Thanks.

Nick
 
hmmmmm... interesting..!

other than that it sounds like a fun fault to play with!! how new is the light? possibly a faulty one from the factory??
 
Last edited by a moderator:
Just got back from my hols and going to look at this light again tomorrow.
Just supplying a direct feed to the lamp won't help much as the problem is created when switch is off and one lamp removed. If I remove the switch from the equation I expect that the luminaires will all go on! I reckon there's an induced voltage somewhere along the switch wire. I'm gonna create a switch external to the existing and wire it in and try it, whadya think? Also gonna try one of her other multi-lamp fittings and see if that has same problem. I HOPE it's the fitting........

Nick
 
Just got back from my hols and going to look at this light again tomorrow.
Just supplying a direct feed to the lamp won't help much as the problem is created when switch is off and one lamp removed. If I remove the switch from the equation I expect that the luminaires will all go on! I reckon there's an induced voltage somewhere along the switch wire. I'm gonna create a switch external to the existing and wire it in and try it, whadya think? Also gonna try one of her other multi-lamp fittings and see if that has same problem. I HOPE it's the fitting........

Nick

It won't be :eek:
 
Found the cause of the dimming lights, when the smoke nearby is disconnected from the permy live then the problem goes away. Don't know why though, very strange. Any ideas????
Now I've just gotta find somewhere else to feed this smoke from.
 
It was fed from the switchline, then I removed it, tried the new switch cable that I'd run and the job was fine. I then reconnected the smoke to the permanent live and the problem returned........
 
Are you sure you have a perm live from the lighting, because the fault your describing sounds as though your connecting the smoke between the switch and switch return .
 
This might or might not be related, but i recently read in a manufacturers spec that their smoke detector could not be used in a lighting circuit that had fluorescent light fittings. There was no explanation why. I assumed it must be something to do with the inductance or capacitors in the light fittings.
Do Halogen lights have anything similar??
 
sounds like a job i did not long ago!!

customer had new loft insulation fitted!!
installer disturbed a junction box and the live feed for intruder alarm came out!
been the nice installer he was he reinserted the red cable in to the red connector! (how ever he connected to the wrong red bit and actually connected to switch line from the landing light!

outcome!! when light on stairs is on it powers light and charges intruder alarm!
when light off it also disconnects alarm and the battery in alarm powers the light very dimly!

is your smoke doing the same!!! possibly the battery feeding the light!! i would double check the connections!!


may i also add the loft guy also mashed the screw terminals in JB!!! PRAT!!!!
 
Last edited by a moderator:
I fixed the problem in the end. I just fed the smoke into a jb on the same circuit just upstream and hey presto. Very strange, it deffo wasn't the switch wire I was feeding into! One of those mysteries.
Cheers All.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
lights dim when turned off
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
ngoodson1969,
Last reply from
ngoodson1969,
Replies
17
Views
4,497

Advert

Back
Top