I have a problem that has totally mystified myself and my colleagues - hoping someone could shed some light...
Called out to a flat today, where when they put the kettle on the lights flickered and when they turned on the washing machine, the lights went out (but the fuse did not trip).
There was a hager fuseboard (pre 2008) - socket circuits on RCD protected side, and 2 lighting circuits on non RCD side. All looks installed very well. No loose connections. No reverse polarity on supply or in the installation anywhere.
Insulation resistance check on all cables were 299+
Lights are all run from 5a sockets (no ceiling lights), and wall lights for hallway.
I did continuity tests between neutrals, earths and lines with the MCB's and RCD's off, nothing unusual.
However...
When I tested continuity between each side of the MCB on the Hob circuit with the RCD off and MCB off I got an open circuit, but with the RCD ON and MCB off, I was getting a closed circuit with 700+ reading. With the RCD on, and all MCB's off, I got continuity between the lighting circuit line and the Hob circuit line.
What does this mean? Surely I shouldn't be getting continuity between 2 line cables on 2 different circuits on seperate sides of the fuseboard even with the RCD on?! What does this mean?
Anyone ever seen or heard of this before....
You're thoughts are gratefully received, because I left the customer with the Hob circuit MCB off and the lights were ok with no flickering when pulling power on the sockets. I would like to get their hob circuit back on without it causing problems for the lighting circuits!
Thanks
Kelly x
I have a problem that has totally mystified myself and my colleagues - hoping someone could shed some light...
Called out to a flat today, where when they put the kettle on the lights flickered and when they turned on the washing machine, the lights went out (but the fuse did not trip).
There was a hager fuseboard (pre 2008) - socket circuits on RCD protected side, and 2 lighting circuits on non RCD side. All looks installed very well. No loose connections. No reverse polarity on supply or in the installation anywhere.
Insulation resistance check on all cables were 299+
Lights are all run from 5a sockets (no ceiling lights), and wall lights for hallway.
I did continuity tests between neutrals, earths and lines with the MCB's and RCD's off, nothing unusual.
However...
When I tested continuity between each side of the MCB on the Hob circuit with the RCD off and MCB off I got an open circuit, but with the RCD ON and MCB off, I was getting a closed circuit with 700+ reading. With the RCD on, and all MCB's off, I got continuity between the lighting circuit line and the Hob circuit line.
What does this mean? Surely I shouldn't be getting continuity between 2 line cables on 2 different circuits on seperate sides of the fuseboard even with the RCD on?! What does this mean?
Anyone ever seen or heard of this before....
You're thoughts are gratefully received, because I left the customer with the Hob circuit MCB off and the lights were ok with no flickering when pulling power on the sockets. I would like to get their hob circuit back on without it causing problems for the lighting circuits!
Thanks
Kelly x