The problem is all the lights in the house are on a 6 amp type B MCB (new wylex) the approximate load is 2.5kw – 3kw and every time a bulb goes the breaker trips out. It’s not on the RCD side as the CU only has one RCD which the sockets up and down are on.
Please can you give me any advice on how to solve the problem do I just split the load of the light to up and down on two separate breakers?

Many thanks
 
Where do you get 2.5kw - 3kw from as this would equate to 10 - 13amps, are you allowing for diversity when calculating lighting load???

Its common for incandescent lamps (filament type) to trip standard mcb's when they blow its just something to put up with or change to CFL low energy type they done suffer this side effect.
 
Last edited by a moderator:
3kw at 230 volts givs you 13 amps!!!! the mcb will be slowly heating up if you had all the lights on, when a lamp blows it causes a momentry fault that most MCBs can handle as their not run at such capacity, in your case your running over capacity and the slightest upset, like a lamp blowing is causing the tripping. only real solution is to spread the load across circuits.


Edit to add what darkwood just put,, CFL lamps will help here
 
Last edited by a moderator:
3kw at 230 volts givs you 13 amps!!!! the mcb will be slowly heating up if you had all the lights on, when a lamp blows it causes a momentry fault that most MCBs can handle as their not run at such capacity, in your case your running over capacity and the slightest upset, like a lamp blowing is causing the tripping. only real solution is to spread the load across circuits.
I suspect OP hasnt calculated lighting load correctly and as ive just mentioned and may i correct you in your assumptions that the mcb is more readily tripping due to mcb been up to capacity, when a incandescent lamp blows the filament is vapourised leaving an ionised trail in the gas which is a more or less a short circuit hence you see a bright flash as the lamp pops - this is an electrical arc flowing through the ionised gas with no resistance, normally the gap between the filament stalks would require several thousand volts to cause a spark to jump across but the white hot failing filament has already created a path so allowing 230v to jump this gap at the expense of the mcb seeing the short circuit, whether the mcb had no load or was fully loaded it would still react to this as a short circuit and trip.
 

Reply to Lights tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top