How many circuits does the installation have?
You can't just do an overall IR test of the installation and claim it needs a rewire based on a reading of .4M
You may for example have 5 circuits that have an IR of 2M each which would give you an overall IR of .4M
This also depends how many cores are in each OCPD, and how many spurs are present. Could be absolutely nothing wrong with these cables - or equally as likely IMO, one leg of one circuit bringing the whole installation down.