Just tested a lighting circuit to find that the voltage between Line and Neutral was 240V and Line to Earth was around 70 volts? What could this be? a short between Line and Earth? Also the circuit is on a 6A 30mA RCBO but doesn't trip, the test button works though...

thanks
 
Line to Earth was around 70 volts? What could this be? a short between Line and Earth

Does not compute... you can't have a voltage across a short!
 
Test kit out ,if you have 70 volts between line and earth your earth is possibly open circuit , and if all was ok and you had a line to earth fault i would expect a Bang !!! so you need to carry out an r1r2 test ,ir test etc
 
Just tested a lighting circuit to find that the voltage between Line and Neutral was 240V and Line to Earth was around 70 volts? What could this be? a short between Line and Earth?
A problem possibly but 70V is hardly indicative of a short circuit.
Maybe the neutral not connected to earth so the system is floating?
Have you checked that?
 

Reply to Line to Earth fault 70 volts?!? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
274
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top