I was called to a single phase installation in a pub as the staff were receiving shocks when touching equipment such as fridges water pipes etc. I located a damaged cable where line and PE conductors were touching and causing 240 volts on the entire earthing system at the installation. In other words there was 240 volts PD between the casing of equipment/ water pipes etc and true earth. This was a TT system where the 100ma RCD protecting the whole installation had been removed at some point previously! The ZS reading I was getting was around 2 Ohms. The mystery to me is why none of the MCBs on the installation were tripping out?
I am probably missing something really obvious. Any thoughts/ ideas would be greatly appreciated.
Many thanks
 
Lenny,

Many thanks for your informative reply. The fault was located in a 16mm T/E cable supplying a second DB from the main DB in the installation. The second DB had a variety of 32/20/and 6 amp MCBs. None had tripped. No RCD on second DB. The main DB had a similar variety of MCBs. All MCBs are type B. No RCD on first DB. I resolved the problem by removing the supply cable to the second DB. The pub is closed and will be until a new supply cable is run to the second DB. Thanks again for your comments
 
Hi Spinlondon,

Thanks for your reply and the information about low/high impedances. many thanks.
The fault was in a 16mm t/e supplying a second DB from the main DB. Both DBs had a variety of type B MCBs but no RCDs. 6,20, 32 amp MCBs. The only RCD on the installation had been removed and it was a 100ma unit located at the DNO incomer point. The pub is closed until a new RCD is installed and a new supply cable from DB1 to DB2. DB2 has been isolated by disconnection the supply from DB1
Cheers
 
Lenny,

Many thanks for your informative reply. The fault was located in a 16mm T/E cable supplying a second DB from the main DB in the installation.

There we go then, large OCPD's need low loop impedances to disconnect under fault conditions which you dont ordinarily get on a TT system hence the requirement for an RCD.

Take that RCD away and..........
 

Reply to Line to earth fault but MCBs will not trip..Why? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top