A
ASHEED
I HAVE Dyn11 650KVA, 4160/415V ,60 HZ . Y STAR POINT EARTHED.
SMALL D.B FEED A CAMP ( LIGTHS, A/C'S, WATER HEATER ....ect)
DISTANCE FROM D.B TO CAMP 1500 MTR.
CABLES :
3 ( 3C X 2 AWG), 5KV CABLE ,3 CABLES EACH CABLE USED FOR (R S T), 5 KV CABLE BUT USED FOR 415V
1C X 95 MM2, USED FOR NEUTERAL
LOAD: 40 - 60 KW
PROBLEM
WHEN CABLES LOAD :
CURRENTS UNBALANCE , NUTERAL CURRENT VARIED 9 -27 A, ACCORDING TO LOAD
BEFORE CONNECTED (N TO G ) AT LOAD & D.B SIDE N-G VOLT 9 -12 V.
L- L VOLTAGE CONSTANT AT LOAD SIDE 415V
L - N VOLTAGE VARIES 208 - 285 V (NOT CONSTANT 240V), CHANGE ACCORDING TO LOAD.
L - N VLOTAGE MOST TIME CONSTANT IN TWO PHASE BUT THE THIRD PHASE L - N CHANGE AND REACH TO 280V AND DOWN TO 240, 250, .... VOLT. AND SOME TIME VOLTAGE TO NEUTERAL FLOATING IN TWO PHASES.
WHY V(L-N) FLOATING WHILE V(L-L) CONSTANT?
HOW TO SOLVE IT?
NOTE: WHEN I CONNECT( G - N )IN D.B & LOAD SIDE NOTHING CHANG BUT THE FLOATING DECREASE.
REGARDS;
ASHEED
SMALL D.B FEED A CAMP ( LIGTHS, A/C'S, WATER HEATER ....ect)
DISTANCE FROM D.B TO CAMP 1500 MTR.
CABLES :
3 ( 3C X 2 AWG), 5KV CABLE ,3 CABLES EACH CABLE USED FOR (R S T), 5 KV CABLE BUT USED FOR 415V
1C X 95 MM2, USED FOR NEUTERAL
LOAD: 40 - 60 KW
PROBLEM
WHEN CABLES LOAD :
CURRENTS UNBALANCE , NUTERAL CURRENT VARIED 9 -27 A, ACCORDING TO LOAD
BEFORE CONNECTED (N TO G ) AT LOAD & D.B SIDE N-G VOLT 9 -12 V.
L- L VOLTAGE CONSTANT AT LOAD SIDE 415V
L - N VOLTAGE VARIES 208 - 285 V (NOT CONSTANT 240V), CHANGE ACCORDING TO LOAD.
L - N VLOTAGE MOST TIME CONSTANT IN TWO PHASE BUT THE THIRD PHASE L - N CHANGE AND REACH TO 280V AND DOWN TO 240, 250, .... VOLT. AND SOME TIME VOLTAGE TO NEUTERAL FLOATING IN TWO PHASES.
WHY V(L-N) FLOATING WHILE V(L-L) CONSTANT?
HOW TO SOLVE IT?
NOTE: WHEN I CONNECT( G - N )IN D.B & LOAD SIDE NOTHING CHANG BUT THE FLOATING DECREASE.
REGARDS;
ASHEED