Just looking at an oldish crabtree board and found two 32amp mcb's with 6mm cable on each linked with a 10mm on the outgoing side. This goes to a shower unit with 63amp rcd and 50mcb. Is this ok? I know it's not an ideal solution but is it safe? Shower is 11kw

Any advice would be good thanks
 
are you saying that you've got 2 MCBs parallelled up, feeding a shower?
 
think about it. turn off 1 mcb to isolate shower, you still got power to it through the other mcb. it's a definite NO. 11.5 kw is 50A, so it needs sorting ASAP. you should be OK with a 50A mcb. measure the actual current drawn with a clamp meter. probably be around 42 - 45A
 
Last edited:
This is what I thought! I reckon it's been done as it is an old type board and you can't get type 1 breakers! I know what the customer will say! "it's worked fine without any problems just leave it" what a pain! Anyone know where I can get a crabtree type 1 50amp mcb?
 
are they starbreaker MCBs? i,ve got some, not sure what values. can you upload a pic?
 
only solution then is to split the tails, fit a separate CU with RCD and 50A MCB or RCBO. i would disconnect from existing MCBs if he won't pay for this. or get him to sign a disclaimer. end of.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Linked MCB
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
nrg,
Last reply from
davelerave,
Replies
10
Views
1,664

Advert

Back
Top