Advice please .Is it ok to put a junction box into a ring main then from that put a fcu with a 13amp fuse for a cooker hood, then from that fcu put another fcu with a 5amp fuse for 2 under cabinet strip lights using the correct size wires etc ?
 
well spotted, geordie. a 5A would be ideal for the hood, but then he'd need to fit a 3A for the lights to achieve discrimination.
 
well spotted, geordie. a 5A would be ideal for the hood, but then he'd need to fit a 3A for the lights to achieve discrimination.

this would only provide discrinination if the fault was betweem 3A and 5A or there abouts, any fault current will take them both and the mcb feeding them.

we are only protecting the cable and providing a place for local isolation of the fan unit in case it needs to be worked on.

Discrimination is next to impossible to achive in a domestic enviroment with mcb's at the cu.
 
Thanks for replies so I would be able to go from junction box from ring main with 2.5mm wire to fcu then feed off to cooker hood with 5amp fuse then go from that fcu with 2.5mm wire ?? to another fcu then feed off that with 1.0mm wire to two 30 watt strip lights with 3amp fuse
 
If its just info on how the job can be done then that is fine, but you will need to get a local leccy guy/gal in to do the work, as this work comes under Part P and the work will need to be certified.
I also agree with Geordie Spark in post 5 and that 13 amp for a cooker hood seems excessive. The manual for the hood will tell you what size fuse it needs to have.
 
This is at my own house, just needed some advice as I had read different ideas on other websites all giving different opinions to what was right .

Don't matter whos house its at. If you build an extension at your own house, you still need to comply with building regs.

The problem with asking on forums, is people give different answers, some correct and others not so. If you decide to go down the incorrect route and something happens is it worth the hassle?

As its such as simple task and you are asking questions, i'd just get a few quotes and get it done right.
 

Reply to Linking two fused connection units from a junction box in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top