G

gaulty

little help on insulation resistance. although i have my 2391 it's been around 3 years since i've tested and have just start a new job where a lot of it is involved.

Instead of disconnecting every emergancy light etc when meggering out a circuit can you twist together the live and neutral of the circuit your testing together at the board then proceed to test between live/neutral and your cpc without disconnecting voltage sensistive equiptment or have a got it completely wrong.

Im sure i read somewhere that this was an alternative method when disconnecting lights etc was not an easy option. My gaffer on site said just test to the light switch but I'm not happy doing that for obvious reasons :eek:

Thanks in advance
gaulty.
 
Yes mate. And mark it as a Limitation on the certificate too. Dont forget to drop it to 250 volts either. However, as the L+N are joined together, no current can flow and therfore no damage to the appliance, however, opinions seem to be divided on this so play safe and test at 250 volts.
Should be tested with all light witches on so that wiring is included in the ir test.
I carry in the van a couple of the normal reference books, osg, etc, which clearly outline these procedures, well worth having mate.
 
Last edited by a moderator:
Initially test at 250V then if it's all sweet crank up to 500V remember to mark it as LIM on Line/Neutral column and note on cert.

Also test 2 way switches in all positions.
 
thanks mate was 95% sure you could do it that way just the gaffer had never heard of it and had me doubting myself. Thanks again
 

Reply to little help on insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top