Brief run down for you all

Checked end to end of ring that’s sound
Meggered LN sound NE sound LE 0.03

Split the ring same stuff
Split it again same stuff again

Long story short stripped all sockets off on the ring and every single leg has a LE fault

Was rewired 2010

Only logical thing I can think is just a bad drum of cable was used ?
The CU is a screwfix off brand thing so one can only assume it is screwfix special T&E used

Anyone got a better suggestion please let me know left me scratching my noodle for a while

EDIT:
there are no neons
The cable is twin and earth 2.5mm
All sockets were removed ring completely split at every outlet
 
Last edited:
Any of the following still connected?
neon lights on spurs or switches
surge protected sockets or usb sockets
rcd sockets
rcbo on supply?
 
That is sounding very much like bad cable. Odd it is just the L but presumably it could have been the brown PVC mix that was contaminated in some way.

I wonder if it was like that new and the installer just ignored it, or if it has gone bad with time?

The rented "anti vandal site office" we have just is a bit like that, but all circuits in the 0.2M region for both L-E and N-E even though not much T&E. Not ours to fix though :(
 
Any of the following still connected?
neon lights on spurs or switches
surge protected sockets or usb sockets
rcd sockets
rcbo on supply?
Any of the following still connected?
neon lights on spurs or switches
surge protected sockets or usb sockets
rcd sockets
rcbo on supply?
Every thing is disconnected pal literally just legs out the wall and every single leg has a LE fault some 0.03M next one coul be 0.59M one leg was 3.38M but every single leg was faulting
 
Surge protected extension leads still plugged into each separated section?!
Can you get enough of the T&E to read the manufacturer's details, etc? Wonder if there is ant site with recall information on bad cable.
Not at the minute left my suggestion and findings with homeowner he’s ringing home insurance to see if he can get them to foot the bill 😂
 

Reply to Live earth fault on every leg of the ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
984
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top