Went to put in a new circuit (for a solar inverter) on a property with a TT system (the first time I've encountered one). The existing system is a dog's breakfast with three splits at the after the meter at a Henley block. There's some kind of 60 amp breaker labelled BS 842 in the mix. This may be an early earth leakage device but I don't know.
So I split off from the Henley block again and connected a mini DB with a 30ma/40 amp RCBO. All tests were fine - including a very low ZE (for a TT system) of 0.35, until the RCD test - the thing just wouldn't trip.
Taking the cover off to investigate I brushed my hand on the earth bar - which was live!
After investigation all the earths were live - testing with my MFT and a straight voltage tester between live and earth showed 240v.
I disconnected my entire new circuit and tested again - same result.*
My question is : Have the fuses not blown because there is in fact no path to earth (a long lead test to the earth rod gave a reading of 55 ohms) or am I doing something really dumb?
Chances are it's been like this for a while - the system works merrily along but presumably is very dangerous.
So I split off from the Henley block again and connected a mini DB with a 30ma/40 amp RCBO. All tests were fine - including a very low ZE (for a TT system) of 0.35, until the RCD test - the thing just wouldn't trip.
Taking the cover off to investigate I brushed my hand on the earth bar - which was live!
After investigation all the earths were live - testing with my MFT and a straight voltage tester between live and earth showed 240v.
I disconnected my entire new circuit and tested again - same result.*
My question is : Have the fuses not blown because there is in fact no path to earth (a long lead test to the earth rod gave a reading of 55 ohms) or am I doing something really dumb?
Chances are it's been like this for a while - the system works merrily along but presumably is very dangerous.