Called out to a 1st floor flat in 3 storey 9 flat council block.
Leaseholder was getting shocks of the shower and the shower room floor.
Suspected either static or insulation fault. Lifted saniflo cable and got a shock (just a nip but definitely not static!) when my hand brushed against the pipework and the wall.
Checked with megger and getting extraneous voltages of 50v - 110v between pipework and brickwork/concrete.
Turned of main switch on CU, still getting voltages.
Pulled main 1361 in ground floor plant room.
Still getting voltage readings.
Flat has poor main earth and needs supplementary bonding. Client called the council who sent their own electricians but though they agree there must be some kind of earth fault somewhere in the building arent really helping.
Any ideas? The extraneous voltages with the 1361 pulled has thrown me!
Steve