mickytuff

Hi all, i need the calculation applied to work out the current per phase for a 3 phase circuit.
Found a 9.1 kwatt heater on a 25A triple pole mcb (60898), so on single phase load divide by volts = amps, but this is not the case for 3 phase, any help much appreciated?????
Oh i found the heater on a hospital periodic, the cable used was a 4 core 2.5mm armoured...............
 
Just in fun (not a dig at you P&S) I worked out the PF that would be required to get 23A for 9.1KW @ 400V. It comes out at a staggering 0.375 lagging.

I’ve only ever seen figures like that on huge induction furnaces (they had massive capacitor banks linked to them). The cables had that much current flowing through them they had to have water pumped through to keep them cool.


As I said I did it for fun as I like playing around with maths.
 
Last edited by a moderator:
i was testing this circuit as part of a periodic on the hospital, saw the cable size feeding this heater rated at 9.1 Kwatt and looked a bit on the slim side copper size wise, but couldnt think of the calculation required, thanks for your help as alaways its good to discuss )))))
 

Reply to Load calc for 3 phase supply?????? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
823
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
906

Similar threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
654
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top