load question | on ElectriciansForums
Discuss load question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
W
wolfiehogan
hi guys am trying to work out a question with no luck. if i have a single phase load say30 kva how do i work out the load per phase if i was to split the load over a phases.
split over 3 phases would be 10kVA per phase. so on 415V, 10,000/240 = 41.67A
Basic calculation...
I = P ÷ (V x √3)
I = 30,000 ÷ (400 x √3)
I = 30,000 ÷ (400 x 1.73)
I = 43.35A per phase
Reply to load question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
They do a cy type with pur coating and it is even tougher but is shielded