Hi
I completed a job recently where a hotel reception had a new desk fitted. The old desk dado was supplied via an RCD spur from the existing ring. This ring is fed from one of the very old Merlin single phase boards which I’ve been told you cannot retrofit Schneider ic60n RCBO’s in. I had to remove a couple of sockets including the existing Rcd spur from a wall backing on to a riser as the new desk needed to be flush to this wall. The existing ring was fed in pvc tube down the riser and rear entry to the sockets. Instead of using an Rcd spur to protect my alteration at this point (x4 sockets 2.5 radial in dado) is there a regs issue with instead fitting a single module plastic enclosure with a B16 RCBO - no main switch just the ring terminated straight into the RCBO? - circuit is supplied via C32 MCB. (Enclosure mounted in the riser with 2.5 LSF glanded out the bottom and penetrating the wall through to the desk dado.

Interested to hear thoughts on this.
Thanks
 
I wouldn't see any problem either, but ...
If you look in the book it says you can use BS1363 devices on an RFC - it's one of the conditions for having an RFC where the CCC of tbe cable is lower than the rating of the circuit protection.
We then get into semantic arguments. If the regs say you use BS1363 devices, does this implicitly prohibit other devices ?
 
I wouldn't see any problem either, but ...
If you look in the book it says you can use BS1363 devices on an RFC - it's one of the conditions for having an RFC where the CCC of tbe cable is lower than the rating of the circuit protection.
We then get into semantic arguments. If the regs say you use BS1363 devices, does this implicitly prohibit other devices ?
Who knows? There's this, in the OSG app H:

"Permanently connected equipment should be locally protected by a fuse complying with BS 1362 of rating not exceeding 13 A or by a circuit-breaker of rating not exceeding 16 A and should be controlled by a switch, where needed (see Appendix J)."

Based on that, I suppose the IET aren't completely against the idea of using MCBs on ring finals.
 

Reply to Local RCBO protecting ring final alteration. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
693
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top