I do a lot of domestic bathroom refurb's. Sometimes its as little as replacing the main luminaire.
As regards additional protection by RCD, I sought some guidance from my scheme on RCD requirement, when doing as above. And was confirmed that a like for like replacement of luminaires or accessories, in an existing install, did not require additional protection by RCD (supplementary bonding in place if necessary).
I have one to do in a week, replacing down light & extractor fan in ensuite. However, they have an existing shaver socket, they want relocating. There is a cupboard, outside zone 2, in which there is an existing circuit (no RCD) supplying a luminaire, which will become redundant. I was contemplating using this to supply the relocated shaver socket?
Wadda do ya think? Or am I over complicating things
As regards additional protection by RCD, I sought some guidance from my scheme on RCD requirement, when doing as above. And was confirmed that a like for like replacement of luminaires or accessories, in an existing install, did not require additional protection by RCD (supplementary bonding in place if necessary).
I have one to do in a week, replacing down light & extractor fan in ensuite. However, they have an existing shaver socket, they want relocating. There is a cupboard, outside zone 2, in which there is an existing circuit (no RCD) supplying a luminaire, which will become redundant. I was contemplating using this to supply the relocated shaver socket?