I do a lot of domestic bathroom refurb's. Sometimes its as little as replacing the main luminaire.

As regards additional protection by RCD, I sought some guidance from my scheme on RCD requirement, when doing as above. And was confirmed that a like for like replacement of luminaires or accessories, in an existing install, did not require additional protection by RCD (supplementary bonding in place if necessary).

I have one to do in a week, replacing down light & extractor fan in ensuite. However, they have an existing shaver socket, they want relocating. There is a cupboard, outside zone 2, in which there is an existing circuit (no RCD) supplying a luminaire, which will become redundant. I was contemplating using this to supply the relocated shaver socket?

Wadda do ya think? Or am I over complicating things :)
 
Tricky one........

Like for like - comment on invoice

Relocating the shaver point - I would be inclined to be stricter and insist on the RCD
 
The bathroom is defined by walls, floors, ceiling, doors and fixed partitions, etc. therefore you can (possibly) consider the cupboard to be outside of the bathroom and not require RCD protection to the supplying circuit (so long as the circuit does not also feed the bathroom or pass within the walls of the bathroom).
A shaver socket on its own (not the supplying circuit) would not need 30mA RCD protection as it is protected by electrical separation rather than ADS.
However I would supply the 30mA RCD protection anyway if practical to do so.
 
The actual fix is quite easy, the mcb can be replaced with an RCBO. The current shaver socket is adjacent to the sink, would be moved into a cupboard to another existing circuit on an mcb, almost like, 'like for like'.

Thanks for the advice, I had emailed my scheme, I'll report back with their advice.
 
If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met.
 
If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met.

But that's the rub, I'm not extending it. I'm disconnecting the luminaire and reconnecting the shaver socket?

Edit; supplementary bonding is only required if something is extraneous :)
 
But that's the rub, I'm not extending it. I'm disconnecting the luminaire and reconnecting the shaver socket?
Thought you were relocating the shaver socket ie moving it to another location in the bathroom.
Fed of the lighting I would guess?
 
sorry your honour, i was only moving i tand never thought of fitting a RCBO till i read the local rag and saw my customer was brown bread.
 
But that's the rub, I'm not extending it. I'm disconnecting the luminaire and reconnecting the shaver socket?

Edit; supplementary bonding is only required if something is extraneous :)
All circuits in the location would still need supplementary bonding together regardless if associated pipework was plastic if no rcd protection was afforded
Really only a shower and lighting I suppose normally
 
Thought you were relocating the shaver socket ie moving it to another location in the bathroom.
Fed of the lighting I would guess?

Sorry its difficult to describe. Existing shaver socket point needs to go. Customer still wants a shaver socket, doesn't want light in cupboard anymore (it's bathroom furniture, not a walk in cupboard), so I will disconnect light and reconnect shaver socket to it. The old light was on it's own separate circuit (for some reason), it's whether I leave it on mcb or convert to RCBO.
 
All circuits in the location would still need supplementary bonding together regardless if associated pipework was plastic if no rcd protection was afforded
Really only a shower and lighting I suppose normally

I don't see the point of bonding a plastic pipe?
 

Reply to Locations containg a bath or shower - Additional protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
282
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
792

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top