Hi everyone,

I have just got back from my friends place, he is doing a loft conversion. i noticed that he has run the new wiring for the lights and ring main out. but my concern is that he has run it under the new joist and on top of the insulation. For the lighting circuit it is between the insulation and the eves of the roof.
I thought you had to run the cable clipped to the joist and drill a hole through where required and to keep it away from the insulation.

i thought i should just check before he got to the point of no return.

Thanks
 
As long as cables are of the correct size to cope with being immersed in insulation then fine, on the point of clipping, some might argue that if you clip it to every joist, A- You can't use them as draw wires in future and B- they are more likely to be hit when plasterboarding. I woulde go with the general rule of making sure they are secure enough to be not drooping all over the place.
 
As Somerset says, as long as the cables have been correctly selected then it should never be a problem. Is your man a spark? If so then he should have a common sense approach to his cable routes, if he isn't well I hope he's lucky.
 
The cables were 2.5 and 1.5. he has done a short course as far as i'm aware.
The cable aren't dropping. The 2.5 is under the new floor and obviously the 1.5 is in the roof space.
 
Hi everyone,

I have just got back from my friends place, he is doing a loft conversion. i noticed that he has run the new wiring for the lights and ring main out. but my concern is that he has run it under the new joist and on top of the insulation. For the lighting circuit it is between the insulation and the eves of the roof.
I thought you had to run the cable clipped to the joist and drill a hole through where required and to keep it away from the insulation.

i thought i should just check before he got to the point of no return.

Thanks
look in the OSG for cables run in more than 500mm of insulation....
then de-rate the cable accordingly....
seemples...
 

Reply to loft Conversion in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

im just assuming that they are designed to be surrounded by material, and would heat to a certain amount, spreading the heat into the material...
Replies
4
Views
235
Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top