Hi Guys rewiring a flat 2 bed small flat the sockets in the bedrooms lounge cables will go through the roof which will get covered in hairy mearey if I deceide to ring main it whill I be able to use a 20mcb or shall i do a 4mm radial on a 20mcb cannot rember the derating factor for cables covered in insulation thanks
 
If it's covered for more than a metre (in total) then you derate by 50%, so a 2.5mm T&E normally good for 27ish amps becomes 13ish. Derate protection devices accordingly.

Remember though that methods 100-104 allow for insulation and if the cable is laying on plasterboard ceiling/clipped to stud/joist and just covered (on one side) in insulation then it's still method C and you don't have to de-rate.
 
Ok cool owner says he might be getting loft insulated after we leave so for the job we will take this as a yes havent rewired a flat were all cables run through loft for years so had to get my thinking cap on and its late we just going to fit a 20amp radial for small power in 4mm
 
if the cable is laying on plasterboard ceiling/clipped to stud/joist and just covered (on one side) in insulation then it's still method C and you don't have to de-rate.
Is this not method 101 or 100 and is derated to 21 or 17 amps respectively for 2.5?
This would mean that insulation covered 4mm with cable touching the inner wall and >100mm insulation would be derated to 22A and you could not use a 32A breaker on such a radial.
 
Use running boards and keep the majority of the wiring clear of the stuff....doesnt take much longer,just spike some 6x2's or something above the level of any insulation.
 
Agree with wirepuller here, keep the cables above the insulation level and you'll be fine. You can even use a small sized wire-basket to span the joists etc!!! That stuffs cheap enough, and makes the job look a little more professional too, ...Perfect for taking the scam assessor to see...lol!!!
 
I must of been up hundreds of lofts that have 2.5mm ring finals absolutely covered in insulation and been like that for many years.Never heard of or came across any melted cables or shorts yet!
 
I have always been a bit confused about loft insulation and the regs.

the regas state that table 52.2 is based on a value of 0.04 Wm-1 K-1, basicly 1 m2 of insulation will let 0.04w/degK through it.

loft insulation as detailed below has a value of 0.16Wm-1 K-1 so that will let 4 time the amount of heat through that the regs are calculated on, so i'm not sure "loft insulation" cannot be called "thermal insulation" with regards to the regs.

Loft Roll 270mm

I am happy to be put right on this if the above is wrong.
 

Reply to the thread, titled "loft insulation" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top