M
mpelec
Hopefully someone can answer this query for me.
I'm more used to domestic installations but have taken on a job in a workshop. The workshop is around 80m away from the intake which is a 3 phase TN-C-S supply. The workshop is new but I'm using an existing 16mm 4 core SWA cable. I'm using the SWA as the earth. The ZE at the origin is within limits but when measured on the workshop DB I get 0.70 ohms, I'm guessing due to the length of cable & that I'm using steel rather than a copper conductor.
When measuring ZS at the sockets etc I'm getting a higher reading than those allowed in table 4.1.2 of the regs for type c rcbo's. If I changed the rcbo's for type b's the readings would be within limits but I'm worried they would trip with an inrush of current.
Any ideas? Thanks, mpelec.
I'm more used to domestic installations but have taken on a job in a workshop. The workshop is around 80m away from the intake which is a 3 phase TN-C-S supply. The workshop is new but I'm using an existing 16mm 4 core SWA cable. I'm using the SWA as the earth. The ZE at the origin is within limits but when measured on the workshop DB I get 0.70 ohms, I'm guessing due to the length of cable & that I'm using steel rather than a copper conductor.
When measuring ZS at the sockets etc I'm getting a higher reading than those allowed in table 4.1.2 of the regs for type c rcbo's. If I changed the rcbo's for type b's the readings would be within limits but I'm worried they would trip with an inrush of current.
Any ideas? Thanks, mpelec.