Hi everyone.
I'm an electrician in Leeds and i'd really appreciate your view on walking away from jobs when the existing install is not right.
For instance I had two days booked in for a CU change and rewiring of some spotlights. I always start a CU change by doing a condition report first on all circuit attached. Within 10 minutes of testing I knew I was going to have a bad day! The kitchen lights were wired to the 32A upstairs socket circuit and no fused spur protecting the smaller cable, I had a neutral to earth fault on the lighting circuit, there were multiple DIY alterations, there were multiple spurs taken off the ring without being fused down and the list went on!!
At this point I advised the customer there were multiple issues and I would be unable to fit the consumer or rewire the spotlights.
I advised the customer that the property needs rewiring, to which I got the standard response of 'well it works so I will just leave it as it is'.
This was yesterday and I am now sat at home today with losing a day and a half's pay with only being able to charge for the condition report.
This for me is happening way too often with not being able to carry out planned works due to the poor existing install.
I would really appreciate knowing how everyone else deals with these situations? Do you do the same as me and walk away meaning you are constantly loosing money or do you just do the work and leave the customer with a dangerous situation report or something to that affect?
Would love to hear you thoughts and opinions on this please.
With a CU change I usually try and do the pre-work testing/EICR at least a few days before I change the CU, that way if any issues come up and the customer doesn't want to proceed with the necessary remedial work I have time to book some other work in/move jobs about. Also, regardless of whether I think a rewire is the best option, I also provide a detailed written explanation of any C2s and FIs and price up the cost of doing the remedials and present that to the customer as well (its an extra hour of work but it helps build trust with the customer as they are less likely to think I'm just trying to make money).
Thanks for the reply. I think I'm definitely going to start booking in the condition report well before the consumer unit for this reason.
May I ask you what do you do personally in other situations like if you were to install spotlights in a room but you come across a fault on the circuit. Would you do the work and leave a dangerous situation report or would you tell the customer that the work could not be done until the fault is rectified?
Reword the contract to cover all eventualities.
You can do the work and in 99% of the time it will be fine but it's that 1% that can get you 5 years in prison.
Thank you for your response. What do you personally do in these situations? Do you do the work and give a dangerous situation report or do you walk away losing money?
I can't answer that question as I left the game many a year ago and went in to IT, I learnt one thing that when you work for yourself always have a contract, contract law trumps everything as it is an agreement between two parties.
Also you have your standards, better to lose money then to compromise, the customer will just get a Electrical Trainee Eastern European to do the work as he is cheap, when his family dies in a burning house at least your conscience will be clear.
There are some situations where I have covered my rear and for instance where a 32 amp ring spur is feeding more than one socket I put a 16amp mcb in instead of a 32amp and made the customer aware verbally and via email/in writing what I have done and what it requires to be corrected and a 32amp mcb fitted, so the job still gets done and you get paid and you have left it safe.
I appreciate that this isn't always possible though, and some will disagree but I can live with it
If it was a fault (rather then say a socket in the same circuit that's in a bathroom or too near a kitchen sink for example) I'd address the fault. If it was easy to determine that it would likely only take a couple of minutes to find I'd find it before raising it with the customer (unless it involved me going into areas of the property the customer wouldn't expect me to be in). If it was something simple that I could sort in a couple of minutes I'd just do it and get on with the job. I then tell the customer after completing the job that I'd found and resolved the aforementioned issue for them and won't be charging them for it - 10 minutes for free is worth a good opinion as people tell other people when they get stuff for free. If it's the sort of fault that often takes longer to find I stop and talk to the customer at that point. My terms and conditions make it clear that my quotes assume the circuits worked on are in suitable condition and any work necessary to make them safe will be at additional cost. I also usually add a line in the quote email reminding them of that but reassuring them they I'll discuss any such work with them before proceeding.
Not quite sure of the type of fault you are referring to, but if for instance a customer wants their old 12 volt downlights replaced with mains led downlights I make them aware that if CPCs aren't present on the downlights or some of them I will resolve it if it's straightforward or if not then I will only fit integrated fire rated downlights that don't require a cpc. I bring both types of downlights to the job so I am prepared.
Again some people might not agree with me, but in the above example (if there aren't CPCs), I am fitting fire rated downlights that don't require a CPC, plus most of the old 12 volt downlights aren't fire rated, and usually the connections are in terminal connectors that aren't enclosed, so I correct these.
My view is that I'm not adding to the circuit, just replacing what was there and leaving it safer than when I arrived.
If it has
Again some people might not agree with me, but my view in the above example (if there aren't CPCs), I am fitting fire rated downlights that don't require a CPC, plus most of the old 12 volt downlights aren't fire rated, and usually the connections are in terminal connectors that aren't enclosed, so I correct these.
Thank you for your reply.
My question is more, if you can't resolve the fault then and there would you do the work and supply a dangerous situation report or would you just walk away?
If it has
I would walk away and often do.
I probably turn more work down than some sparks would, an example was a customer in a mid terraced house that wanted extra sockets fitted, but she had no RCD protection on any circuits, undersized tails, undersized main earth conductor and no water or gas bond. She was happy to pay for a new consumer unit and the other bits to be sorted, but she had spent a fortune on ceramic floor tiles throughout the ground floor and no way was she having the 10mm water bond run in trunking along the skirting board or clipped to it etc, so I called the NICEIC and explained the situation and that I would be making the existing installation so much safer than it was and I would highlight that the customer refused the water bond to be installed so covering my arse, but the answer was an absolute no it can't be done unless the water was bonded.
I didn't do the job, but I do find it bizarre that I would have made things considerable safer for the customer doing everything but the water bond, but I couldn't do any of it.
I couldn't agree with you more. It's so frustrating that you can't install a consumer unit if the existing installation isn't safe or doesn't comply to regs. There is no argument that you would be making it safer than it is by installing RCD protection. I've been in many positions where the customer just can't afford remedial works or a rewire so I can't fit a consumer unit. They are left living with the dangerous installation with no RCD protection on top. I honestly believe this needs to change.
I have this on ALL my CU changes and big quotes:
"NB: If problems are detucted during the fuseboard change additional work may be required. Such issues and associated costs will be discussed with you, prior to being implanted"
Never had the clause challenged, nor had any issues when additional work is required.
It's all well and good believing that you are making it safer, but the reality is that Earthing and bonding are critical to the correct and safe operation of any ADS system.
I am definitely making it safer.
Just leaving it as is with no gas bond, no RCDs, not upgrading the tails and earth conductor isn't worth doing unless the water is bonded, so subsequently absolutely no part of it is made safer??
A consumer unit change will also often highlight potentially dangerous issues with an installation, so who knows what condition the installation is in because without a water bond being connected we won't find out (until the worst happens).
My point is that the fundamentals are wrong if Earthing and bonding aren't there - and I suspect this is what the NICEIC were relaying to you.
Thanks for your reply. My question was more, if the customer wasn't prepared to pay for remedial works then would you just walk away losing money or would you fit it so you get paid but leave a dangerous situation report of the issues?
By inserting this into your quotes should then make people realise that a fixed price quote isn’t possible.
If the customer isn’t happy about the clause then don’t take on the work ....
So I either do these jobs with this clause and customer understanding, or I don’t start. It’s that simple
But if it’s 1/2 hours work and necessary, I would probably do it as part of the job and not pick a fight with the customer ......
My terms state that rectification of any existing faults is not included. That's has always been suffice for quick to rectify faults. Surely you must have been in a position where you've done the pre inspections on a fuse board change and the circuits have that many issues that
In my terms I do have ' rectification of any existing faults are not included'. This has been fine for quick and easy to fix faults but anything more than that I find allot of customers don't want to go ahead.
If a decent visual suggests issues lurking I normally insist on an EICR - full or part to be done and paid for before the CU change
Again, if the client won't accept this, I won't get involved ...
I totally get where you are coming from and you just want it right. For someone like yourself, I would say a better middle ground solution would be to do more investigation and even some testing at survey stage. It will take more time but you will know what you are in for if you then get the job and, on aggregate, should be better off in the long run with not having "no work days" with short notice.
You obviously work in the rich suburbs around Woking and not on Goldsworth Park ;) PS Please don’t take offence if you live there :oops:
If I can instantly see that there is no water bond and the customer refuses to have one (for the reasons previously stated) then no more investigation or any testing is necessary (I think you may have quoted the wrong person).
If it was just remedial work then i think the customer would have been fine with that but there were too many issues that came up when inspecting the property. I was only happy to recommend a rewire which the customer wasn't in a position to do.
Like some others have stated, I always do a few checks prior to giving a quote to established at that least the basics are covered and also have it written on all quotes that it is subject to the existing installation being fit for purpose, that testing/investigation may find major electrical installation faults that will be quoted for separately.
I will normally put right small issues free of charge, however will inform the customer of these beforehand so that they are aware of work that I am completing.
I think in most cases if you explain the situation and gain the competence of the customer then it won't be a problem, there is without doubt always going to the odd one, but in all fairness when I first go and look at the work required I can pick up on if they are reliable to have the extra done or not.
I have walked away from work when they say that they aren't prepared to pay for putting right the issues I find on first visit for quote and make a point to them that any decent electrician will tell them exactly the same as me
The other issue about no bonding would be that the owner might feel that everything is ok now, and everything looks new, whereas with the old installation in place it keep the pressure on to have it done properly as everything still looks rough. You also never know if the person is just tarting it up to sell therefore leaving the new owner with a much less obvious danger.
Although in my opinion adding an up front rcd would probably be the happy medium if the regs were to allow it
The lady in question had spent a small fortune doing her house up and having lovely ceramic floor tiles fitted throughout the ground floor and I very much doubt she was selling it, and I'm sure she will have still have the same unsafe set up.
I am not specifically criticising the NICEIC because that's how it is, but regardless of what regs people point to, carrying out a full inspection of all circuits, fitting RCDs, upgrading the tails, main earth conductor, bonding the gas etc has to better than doing absolutely nothing because the water can't be bonded.
Let's hope doctors don't adopt the same criteria if I have a serious road accident (they could have revived me, but they wouldn't have been able to save my little finger so they let me die because they couldn't fix everything).
I'm 100% with you on this one. This needs to be changed.
True but there are so many ways to think about it. Maybe 9 out of 10 customers who refuse bonding would accept once they are refused to have any electrical work done whatsoever by 3 different electricians. Whereas if all 10 had the rest of the work done then none of them would bother. I think there's an element of bigger picture benefits as well, not saying it's always right but it's nothing like doctors there's no British standard for a human body
That is a fair point.
The water can be bonded. Its just the potential customer doesn't like any of your options. Earthing and bonding come first, then everything else?
Leeds
LOSING MONEY WHEN WALKING AWAY FROM BAD JOBS
Happychappy,