Basically the circuit is of of an air heater battery consisting of : 3 x 2Kw heaters wired in star to a 3Ph & N supply , plus a capacitor start 1 Ph motor on L1 phase .
Total amps of heater = 8.5 amps / phase , motor draws 6.5 amps on L1 phase when run separately . But when both are run together the amps on L1 reads 11.5 amps !!!!! .
Any ideas people ?? . Theres something from the dim and distant past about this but dammed if I can remember . Any help or thoughts much appreciated .
 
The motor might draw 6.5 amps until the starter winding is disconnected at full load speed?
 
Had clamp meters on supply to heaters & supply to motor & another one measuring total current of unit . 8.5 amps for heaters, 6.5 for motor , total current 11.5 all measured at the same time & when left running . Motor not running hot & heaters working ok . Brain now running hot !!
 
Had clamp meters ''on supply to heaters'' & '' supply to motor '''& ''another one measuring total current of unit'' . 8.5 amps for heaters, 6.5 for motor , total current 11.5 all measured at the same time & when left running . Motor not running hot & heaters working ok . Brain now running hot !!


How did you measure the total current with one amp meter?? You will not get a coherent reading placing a clamp amp meter around all three phase conductors... You need to check again, checking each phase conductor at a time, to find the actual current being drawn individually and the total current drawn by this equipment.


Only other way, is by use of a 3 phase amp meter, with 3 CT clamps, even then you would need to ensure you incorporate the L1 lead to the fan within the L1 CT clamp
 
Re-check the motor current when running. 1hp should only be about 3.5A. Also remember warm air is easier to move than cold, it makes quite a difference to fan loading.
 
Think vectors and power factor. Highly resistive load of the heater + highly inductive load of the motor means that the total current on the phase is the vector sum of the two. (ie 8.5 amps @ 0 degrees + 6.5amps @ 60 degrees perhaps)
 
Last edited:
Thanks for the replies guys .
My quandary is over the total amps being drawnon L1 , IE motor is drawing 6.5 amps , heaters 8 amps both of which are OK but the total load on L1 is only reading 11.5 amps .All the reading were taken at the same time using CTs & remained constant . Still pondering over the fact that the total load should be 14.5 amps but the meter is reading 11.5 amps , ie 3 amps low .
 
Thats what I thought , but all meters were checked & were found to be ok .
Should add we manufacture heating equipment but don't remember seeing this problem before .
 
The total current in the leg supplying the motor / heater combo is the sum of the currents flowing through the leg.

What you have not taken into account is the fact that the current flowing through the heater is 8.5 amps at a phase angle of zero (due to pure resistive load) and the current through the motor is at a very high angle (almost purely inductive load). The only way you can add these currents is to add them as vectors, and the resulting vector is the proper current. By lag it means that the motor current is lagging behind the voltage (in this case maybe as much as 80 degrees) and the heater current is in phase (angle of zero degrees)

The (rough) sketch below shows this visually and should help you picture it better. The 80 degrees is a pure guess, it is way too late to even consider working out the proper angle so dont flame me if its wrong.
[ElectriciansForums.net] Lost Amps

 
Last edited:
The lagging was the bit the old grey cells had lost after 40 yrs . Even managed to find the old protractor , a few lines & one happy sparky . Many thanks .
 
Ye sorry for being so abrupt on my original response, IIRC I was at work and pretending to work when i posted it. Surprised me at the level of reactive amps in a single phase. I knew they were pretty inneficent, but never realised they were as bad as that. From those values a 3ph Star connected motor would be much more appropriate, probably would drop your amps down to 1.5a per phase.
 
No problem with orig response . Normally we do use 3 phase motors but these units are used by a petro - chem company and they have to be able to run them from a single phase supply if need be ( L1 L2 L3 strapped together) hence the 240V motor . Again many thanks . :)
 
With an unbalanced three phase system the waveforms are likely to be a distorted sine-waves, particularly the heavy loaded phase, Unless you are measuring with a true RMS ammeter your measured magnitudes are likely to be erroneous when the motor is in circuit
 
Last edited by a moderator:

Reply to Lost Amps in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Thanks for that. New motor goes in on Saturday so I will see what RPM and amp readings are with new motor
Replies
18
Views
2K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
  • Question
Thanks for the good info guys, it helps me work out how to connect the machine. Mostly i am inclined to simply replace both 3 phase motors with...
  • Gareth Blackstock
  • Australia
  • 19
  • 4K
Replies
19
Views
4K
I believe that if some how can go up on your wire size from the transformer to your place it would make a huge difference in your voltage...
Replies
9
Views
2K
Hi,i take it that your "amp draw" is measured clamp style,while running? or is it a power monitor? Knowing the stage at which the overload...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks