Hi
A customer recently demolished a green house and erected anew one in the same location. ZThey required that the new green house wasfitted with a 5 foot florescent light 2 13amp double sockets and 2 switchedfused spurs.
This was all to be run back to a new consumer unit which hadto be a 4 way box as the second green house is to be rebuilt next year and theywant the same installation on that site.
Here is my problem and how I see the situation.
The old green house was feed from a board in a potting shedthat was supplied by a 6mm armoured cable that is 86 meters long. The control panelthat feeds this cable is a sub board from the main house and is fed with a20amp breaker.
The consumer unit at the other end where the potting shed isfeeds, a well, potting shed used as a place for breaks for the gardeners eg.microwave, kettle etc and also feeds the second greenhouse a 13 amp doublesocket and a light.
The property is a private estate.
I would like to hear peoples view points on this as I amtold that basically the 20 amp breaker negates the problem of having toincrease the armoured cable size for voltage drop etc.
If I boil a 1 kw kettle the voltage drops 5volts.
A customer recently demolished a green house and erected anew one in the same location. ZThey required that the new green house wasfitted with a 5 foot florescent light 2 13amp double sockets and 2 switchedfused spurs.
This was all to be run back to a new consumer unit which hadto be a 4 way box as the second green house is to be rebuilt next year and theywant the same installation on that site.
Here is my problem and how I see the situation.
The old green house was feed from a board in a potting shedthat was supplied by a 6mm armoured cable that is 86 meters long. The control panelthat feeds this cable is a sub board from the main house and is fed with a20amp breaker.
The consumer unit at the other end where the potting shed isfeeds, a well, potting shed used as a place for breaks for the gardeners eg.microwave, kettle etc and also feeds the second greenhouse a 13 amp doublesocket and a light.
The property is a private estate.
I would like to hear peoples view points on this as I amtold that basically the 20 amp breaker negates the problem of having toincrease the armoured cable size for voltage drop etc.
If I boil a 1 kw kettle the voltage drops 5volts.