Hi i have been working at a 70's prefab bungalow that has no earth reading at 1 socket, it's part of a ring circuit and all readings good end to end from cu r1 0.44 rn o.43 but no end to end on cpc. readings at socket end to end r1 0.44 rn 0.43 but no cpc end to end. have crossed r1 + rn and have proved it to be a ring and no alterations on electrics since built. have checked all cpcs at every socket and all others ok. There's only a 100mm cavity under a ply floor for access. Apparently the houses were bolted together in 2 parts and all electrics were done in the factory, So i am thinking something must be joining them when erected? just seems very strange that readings are so good on L-N but not the earth if there's some sort of loose connection.
 
Last edited by a moderator:
thanks for the reply, never knew that or seen it. There's 2 lives, neutrals and earths at every point and getting crossed linked readings, but somewhere along the the electrics must have been joined together maybe through a jb so food for though.
 
maybe not then
apparently, it got so widespread, that an amendment in the regs came in stating that you could had to have more devices than spurs on a circuit, to stop the over use of JB, and spuring off the ring main.

I'm 44 and it was years before I started my apprenticeship
 
I take it that Zs is apparent at all sockets

If so then possibly the socket with the highest Zs may be the starting point for investigation
It may narrow down your search

By then splitting the ring at that socket and taking the Zs on the other half of the ring,the highest reading on that half may be the linking socket to the other one identified

It may help narrowing down the fault,but if not,it will have served to segregate the two halves for possible conversion to 2 radials


Just editing because the above was a waste of time,I just re read the post and missed that has no earth reading at 1 socket,I'm a muppet
 
Last edited:
Yes zs at every socket, Thinking about just running new earth to that that socket as its the main 1 in the living room where the tv is. I'm a little worried that something is likely to be very wrong on connection somewhere tho and will cause problem on L or N in the future.
 
If there is Zs at every socket,then my post is relevant,thats a relief
[ElectriciansForums.net] Lost cpc at socket
The radials option is possibly the one that will remove any concern,You could take a reading of the neutral as well as the R1+R2 for each



Dont you just love ring faults,open any socket and if the fault is on one,it is always the last to be opened (it matters not where you begin)If its under the floor,its the place that is the most awkward to get to,sparks law
 
Last edited:
you could run a new earth, but I seem to remember that there is a reg stating that all cables need to be earths
(you know because a DIYer could drill through a cable.)
I would suggest open the ring and test between R1 and Rn,
this way you should find the sockets either side of the socket without the CPC.
Then I would rewire those 2 legs.

anyone else have a view on this one?
 
All of the wiring is done below the floor in the cavity and looped up to the socket, but if i replace legs i think it might be hard to disconnect L-N if there is joint boxes somehere, Also had all pipe work was done in a factory and ply put down so with only 100mm cavity it's going to be risky to open up a section.
 
Draw a sketch map of the bungalow, mark all the sockets on the sketch, do a ZS on all sockets marking the readings on the sketch, and somewhere you'll almost certainly see a significant change in the ZS - then look at these sockets, then check the continuity between them.

Fingers crossed you'll find the area to concentrate on.
 
All of the wiring is done below the floor in the cavity and looped up to the socket, but if i replace legs i think it might be hard to disconnect L-N if there is joint boxes somehere, Also had all pipe work was done in a factory and ply put down so with only 100mm cavity it's going to be risky to open up a section.


what cxable has it been wired in?
is it singles or twin & earth

if the factory made the conduits and cable void, maybe you could draw a new cable in using the old cable as a draw wire.
either using singles, or double insulated singels for the neutral and a single core and earth for the live.
I know you can get this type of cables for lighting however I don't know if you can get it in 2.5mm cable
there maybe a conduit cast in concrete. if so
 
do asyou taught at tech.. R1 +R2 at every socket and see where it stops... then go to next socket see if it starts again.... and rub your head walk up and down room , scratch the bald part then go ahhhhhhhhhhhhhhhhhhhh good luck
 
As the bungalow is prefab, it sounds very likely that you have a house wired in what they used to call Octoflex, basically a pre-wired conduit system which used to have plug and socket arrangements at junctions between sections of the prefab. It is most likeley that there is a loose pin on a multiplug somewhere, where this may be is anyones guess. If its a bungalow have you looked in the loft ??? Either that or if its wired in conduit , someone has had a brain fart and miswired the ring. My favourite is option 1 though

Nick
 
Thanks for the reply's, Bungalow is pitched but there is no loft, ceiling just follows the pitch, new carpets are going in soon so when old ones come will chop some floor up.Might buy a fuse finder to try and track it as there's only 100mm cavity that's insulated so wont be able to see much. Bungalow is wired in t&e.
 

Reply to Lost cpc at socket in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top