Hi all,
There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the oven elements will have had a chance to accumulate some moisture. There's a dual RCD consumer unit, the ovens are on separate RCDs. One of the ovens worked fine on all settings from the start, but the other tripped the RCD a few seconds after it was turned on. We reset the RCD and again a few seconds after the oven breaker was turned back on it tripped again. I thought this could be down to moisture in the element. So the next day I managed to get the RCD to stay on for the oven only with all the other breakers off, to get rid of any background earth leakage. I ran the oven with a combination of elements for an hour or so to try and dry them out, didn't trip at all over the period. Then after cooling down and trying to turn it back on (with the other breakers back on as well), the RCD tripped again. So thought it needed more time to dry, repeated the process, more drying time, now it is working fine for the time being, no more trips.
However I checked the earth leakage with a clamp meter, each ovens leaks between 10-25ma depending on what elements are on. Its only the elements that leak, not the cooling fan or fan. So the highest total leakage on the tails I've seen with both ovens on and the fridge/lights/boiler/some sockets on is 56ma. That's basically the limit for the RCDs, 30ma each but of course normally they'll trip lower than that. I'll ramp test them tomorrow.
Just wondering really if that sounds normal at all or excessively high? Also are the ovens likely to leak less as the elements dry fully and get more use? Otherwise (assuming the RCDs are working right) I can definitely see some problems with nuisance tripping occurring !
Thanks for any replies!
There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the oven elements will have had a chance to accumulate some moisture. There's a dual RCD consumer unit, the ovens are on separate RCDs. One of the ovens worked fine on all settings from the start, but the other tripped the RCD a few seconds after it was turned on. We reset the RCD and again a few seconds after the oven breaker was turned back on it tripped again. I thought this could be down to moisture in the element. So the next day I managed to get the RCD to stay on for the oven only with all the other breakers off, to get rid of any background earth leakage. I ran the oven with a combination of elements for an hour or so to try and dry them out, didn't trip at all over the period. Then after cooling down and trying to turn it back on (with the other breakers back on as well), the RCD tripped again. So thought it needed more time to dry, repeated the process, more drying time, now it is working fine for the time being, no more trips.
However I checked the earth leakage with a clamp meter, each ovens leaks between 10-25ma depending on what elements are on. Its only the elements that leak, not the cooling fan or fan. So the highest total leakage on the tails I've seen with both ovens on and the fridge/lights/boiler/some sockets on is 56ma. That's basically the limit for the RCDs, 30ma each but of course normally they'll trip lower than that. I'll ramp test them tomorrow.
Just wondering really if that sounds normal at all or excessively high? Also are the ovens likely to leak less as the elements dry fully and get more use? Otherwise (assuming the RCDs are working right) I can definitely see some problems with nuisance tripping occurring !
Thanks for any replies!