low ac volt reading. | on ElectriciansForums
Discuss low ac volt reading. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A
ambrad
After installing a garage unit i carried out a voltage test at the furthest point of the installation. i got a reading of 112.5 v L-N. I checked it L-E and got 242v.
I ended up back at the rcd and measured the live side and got 242v. When i checked the load side i got 112.5 v. I disconnected the load live from the breaker and got 1125v again. Does this indicate a faulty rcd or could there be some other issue i am missing. Just to let you know the load was only an ac isolater ready for a solar pv system.
Help please.
thanks
sounds like a faulty RCD, on the neutral side. just make sure the connections on the RCD and N bars ar good and tight.
Sounds like the neutral may be missing, take the tests again with an analogue tester you'll probably see the fault a lot more clearly.
Yep, an analogue voltmeter can be worth their weight in gold at times!! lol!! A must have for every electrician, even if it's a cheapish bog basic model.... Just don't throw it about too much!!
Reply to low ac volt reading. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...