Hi
I’m still learning so forgive my stupid question. I’ve been testing a ring main off 4mm/1.5mm singles in metal trunking and conduit. My reading are:
L-L 0.91
N-N 0.90
E-E 0.80

I was expecting my R2 value to be 2.66 x 0.91=2.42

I this purely parallel path related??

many thanks
 
Thanks for the replies guys. Problem is that the singles go into dado trunking drops and no metal clad sockets in the ring. Some have metal conduits bent into the plastic vertical drops and some have metal kopex but none are made of into plastic obviously. Which made me question the R2 value more as if it was parallel earth paths I’d understand the low reading
 
Also remember you only need a few of sockets to have near-zero ohms from the metallic surround to bring the E-E value down. You don't need all to be connecting.

And yes, that does make interpreting the E-E resistance difficult or even pointless. But at least your L-L and N-N and close enough for comfort!
 
If you are saying there is pvc trunking separating the steel trunking and the sockets, and all the sockets are plastic backed, I'd be inclined to do a continuity test between each end of cpc and the steel trunking.
Making assumption this is EICR not EIC is there a possibility someone has 'bonded' the steel trunking using the circuits cpc, or joined the bonding conductor to the cpc at least twice?
 
In a normal RFC (insulated surround) the E-E continuity gives you very high confidence all sockets have CPC continuity. Not absolute, as the CPCs could be twisted and have fallen out of one socket's E terminal, but still good confidence.

In the typical industrial situation (all metal trunking/conduit) you often don't need the CPC as the metalwork is doing the job and, short of major corrosion or stupid plastic-replacement work, is also a very reliable CPC.

But if you have the CPC used for multiple bonds and a mix of plastic socket supports there is really no guarantee that a low E-E reading is verifying (more or less) all sockets' CPCs. The good readings on L-L and N-N suggest things are probably OK, but if concerned you might want to do the figure-of-eight test and check a decent portion of the sockets have good low L-E results on that.
 

Reply to Low End to End R2 value Help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top