Hi guys
I was asked by a customer to have a look at a kiln which had failed its PAT test. There's low L-E and N-E insulation readings on the element itself (several coils inside daisy chained together). Readings were about 0.25MOhm so way too high to actually be in contact with the chassis anywhere. I also traced each coil and you can see it's not touching the case anywhere.
As I don't do PAT testing I wondered if anyone knew the acceptable level of leakage allowed to pass and whether there was a way around this so the customer can continue to use the machine?
It seems to me as if this leakage is probably by design (old machine), and the heat insulation inside the kiln is probably ever so slightly conductive.
Any thoughts? I don't to tell them to chuck it as it seems fine, just obviously was designed before some genius came up with PAT testing ............................
I was asked by a customer to have a look at a kiln which had failed its PAT test. There's low L-E and N-E insulation readings on the element itself (several coils inside daisy chained together). Readings were about 0.25MOhm so way too high to actually be in contact with the chassis anywhere. I also traced each coil and you can see it's not touching the case anywhere.