Low Insulation Resistance Readings | on ElectriciansForums

Discuss Low Insulation Resistance Readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

danielspencer

Hi there,

I have a customer that wants some lights fitted to an existing circuit.

When doing some preliminary testing on the insulation resistance for the circuit, I was getting strange readings. Line/Earth & Neutral/Earth were well over 500Mohms. When testing Line/Neutral, I was getting only 0.5Mohms. Line/Neutral connected together and tested to Earth are also well over 500Mohms.

Some of the lamps are really awkward to get to, and the customer would prefer it if I try not to remove them. I decided to carry out the test with all the local switches in the OFF position.

As far as I can make out all the light fittings are BC with no low energy or SELV fittings in sight.

I know I don't strictly have to carry out and record this test, but if anyone has any ideas why the Line/Neutral reading is so low, I would appreciate the input.

Many thanks:confused:
 
If L/N is low then there is possibly a PIR sensor or something else, un-isolated on the circuit somewhere.

Thats why your L/N - E readings are clear.
 

Reply to Low Insulation Resistance Readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
272
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top