Hello guys,
Got my fisrt NICEIC assessment on Thursday, and to my horror after I fitted an outdoor socket as my minor job, my insulation test results were terrible.
It was a spur off a kitchen ring, so when I dead tested I unplugged all the loads which were on grid switches but left the grid switches on, all sockets had their loads disconnected, washing machine,fridge,extractor fan, dishwasher all unplugged, the only load I didn't remove was the ignitor for the gas hob,I understand that if there are any loads that you cannot remove then you should not test between live conductors as you will get poor readings, but will a hob ignitor really give me 0.05M?
My results Line/Neutral-0.05M,Line/Earth-1.94M,Neutral/Earth-1.95M

Polarity was fine, no voltage drop, Earth continuity fine, Zs of 0.25 and RCD operated within 200ms.
I am worrying about what assessor will say, but if I have identified the problem and record it as such on the minor electrical works certificate, as needing further investigation will that be OK?

I am doing my test, by two probe method,with the MCB off,I am probing between MCB'S and the earth and neutral bars, without disconnecting conductors.
Advice would be greatly appreciated.
 
Reading through your question again
The results you gave,was this for the whole of the installation ?

If the whole installation was tested then the results being below 2 meg ohms,not good
In this case you need to test each circuit individally to find out if this is a combination of circuits in parallel bringing the reading down,or one circuit being the culprit

A minimum reading of 1 meg is required for each circuit

If it was just the kitchen circuit,then without dis connecting the neutral,you will be reading the whole installation value of neutral-earth not just your circuit

To insulation test between live-neutral you must dis connect all loads

Try dis connecting all loads to the circuit and testing with the circuit isolated (live + neutral)
If this cant be done,connect live-neutral together and test to earth to obtain the circuit value,however, the insulation test is an whole installation test,so if possible,test the whole
 
Many thanks,
I am just insulation testing the kitchen ring,with the MCB off, and all conductors still connected in their respective bars and MCB. When you say test with the circuit isolated, do you mean disconnect the live, neutral and cpc conductors and then do the insulation test between live/neutral, live/earth, earth/neutral?
 
I'd disconnect the neutral at the bar to make sure that you weren't getting false readings due to it being connected to earth some point back towards the DNO's end.
 

Reply to Low Insulation Test Results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
280
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top