Hello guys,
Got my fisrt NICEIC assessment on Thursday, and to my horror after I fitted an outdoor socket as my minor job, my insulation test results were terrible.
It was a spur off a kitchen ring, so when I dead tested I unplugged all the loads which were on grid switches but left the grid switches on, all sockets had their loads disconnected, washing machine,fridge,extractor fan, dishwasher all unplugged, the only load I didn't remove was the ignitor for the gas hob,I understand that if there are any loads that you cannot remove then you should not test between live conductors as you will get poor readings, but will a hob ignitor really give me 0.05M?
My results Line/Neutral-0.05M,Line/Earth-1.94M,Neutral/Earth-1.95M
Polarity was fine, no voltage drop, Earth continuity fine, Zs of 0.25 and RCD operated within 200ms.
I am worrying about what assessor will say, but if I have identified the problem and record it as such on the minor electrical works certificate, as needing further investigation will that be OK?
I am doing my test, by two probe method,with the MCB off,I am probing between MCB'S and the earth and neutral bars, without disconnecting conductors.
Advice would be greatly appreciated.
Got my fisrt NICEIC assessment on Thursday, and to my horror after I fitted an outdoor socket as my minor job, my insulation test results were terrible.
It was a spur off a kitchen ring, so when I dead tested I unplugged all the loads which were on grid switches but left the grid switches on, all sockets had their loads disconnected, washing machine,fridge,extractor fan, dishwasher all unplugged, the only load I didn't remove was the ignitor for the gas hob,I understand that if there are any loads that you cannot remove then you should not test between live conductors as you will get poor readings, but will a hob ignitor really give me 0.05M?
My results Line/Neutral-0.05M,Line/Earth-1.94M,Neutral/Earth-1.95M
Polarity was fine, no voltage drop, Earth continuity fine, Zs of 0.25 and RCD operated within 200ms.
I am worrying about what assessor will say, but if I have identified the problem and record it as such on the minor electrical works certificate, as needing further investigation will that be OK?
I am doing my test, by two probe method,with the MCB off,I am probing between MCB'S and the earth and neutral bars, without disconnecting conductors.
Advice would be greatly appreciated.