O

optician

Tested a circuit today(ring) All other tests check out fine.
L-n greater than 200 mega ohms
L-E greater than 200 mega ohms
N-E 15.5 Mohms.
My Question is, could an Appliance eg washing machine, still plugged in but isolated,
cause such a reading?
Thanks.
 
15.5 Mohms isn't that low. What is the minimum IR reading allowed? If you haven't actually pulled the plug out then you are including the appliance in a N-E IR test.
 
agreed. unplug everything unless you have double pole socket outlets. even so, 15meg. is way above minimum allowed.
 
I know 15.5 is still ok (just lower than the other readings).
Access was tricky and could only just reach the switch.
I didn't realise machine would give a reading between N-E.
Will this damage the machine?
 
Thanks for the replies,
Given that 15.5 Mohms is not problem, would you put an explaination on the MWC(in this case) as to why you think it is low?
 
It passes the requirements and is not even close to investigation level so i would fill in the certificate normally with no further explanation. Also as you do not definitely know why it is lower than the others what would you put?
 

Reply to Low IR On N-E in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top