sivoodoo

Im getting Low IR readings between live conductors and earth on a ring main what would be a some reasons for this, Ive had a look to see if theres anything plugged in, but should this matter between live and earth?

Thanks
 
Depends on what the ring is serving. If it's a kitchen then look for the small things like neons and the electric ignition on some cookers. Burglar alarms have also been mentioned before.:)
 
What about Neutral / Earth?

7M ohms is low but still within the regs....

You're just going to have to investigate. Start by splitting the ring in half and taking a reading of each leg (you'll probably find one half is ok and the other gives a low reading again), then split the half that has the low reading and test each leg again, carry on splitting and testing until you find which part of the cable is faulty.

Hope this helps
 
Last edited:
7M suggest to me that insulation has been damged some where, nail or may be fixing screw in one of the outlets, I had dampness in the wall cause a similar problem, as prievoiusly said you best split ring in half and investigating, may be first unscrew all socket front and see if reading improves, tested a house recently and found cable insulation had deterated such that ring read 2.1 M replaced cable reading went upto 100M, it is possible to overload the ring and for a cable to deterate, there were no since of damage, it was not near centraling heating pipe or any other reason other then age and possible overloading.

Let us now how you get on.
 
If old instalation then 7M is likely, have often seen 2-3M on old wiring (talking grey sheath with B&R conductor insulation), age and possible overloads most likely.
As said 7M is within regs so no prob but warn customer that it is low and there might be a problem that needs further investigation. Cert allows for comments, use it.
 
i've had some circuits recently where it was impossible to unplug everything so i done a test between live and neutral together and earth at 250v. i lot of circuits were reading 0.00ohms.
what types of equipment would cause this.
i also had the same readings on lighting circuits where i couldn't remove all lamps/transformers?
 
Also watch out for the central heating as I got caught with the switched fused supply being spurred off the ring and yep Intruder alarms plus smoke heads dont help
 

Reply to Low IR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
As you've found out, there's capacitive coupling between cores which will induce a voltage into other cores when one (or more) is fed with AC. How...
Replies
3
Views
389

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top