doing an Ins resistance test across all circuits at the CU with load bridged out( L-N shorted ) I have a low reading - 1.03M ohm . after investigation found this low reading goes once the boiler spur is isolated .
any one had similar results ?
this is not the first time ive had appliances give low readings , fridge and extract fan also gave low readings on different properties
any idea why ?
 
any appliance with an electronic pcb is liable to give low IR readings. unless you have too many on an RCD< it's not likely to cause tripping problems.
 
doing an Ins resistance test across all circuits at the CU with load bridged out( L-N shorted ) I have a low reading - 1.03M ohm . after investigation found this low reading goes once the boiler spur is isolated .
any one had similar results ?
this is not the first time ive had appliances give low readings , fridge and extract fan also gave low readings on different properties
any idea why ?

Is this for an EICR or fault finding?
 
doing an Ins resistance test across all circuits at the CU with load bridged out( L-N shorted ) I have a low reading - 1.03M ohm . after investigation found this low reading goes once the boiler spur is isolated .
any one had similar results ?
this is not the first time ive had appliances give low readings , fridge and extract fan also gave low readings on different properties
any idea why ?
remember your only testing the installation up to the fused spurs, this is something that should be mentioned on the test cert. all items after that should be disconnected.. Nothing like sending 500v into a boiler PCB...
 

Reply to low M-ohm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top