Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC 5.75 kA.
Obviously this is a three phase supply, so shouldn't they have doubled the PFC and reported it as 11.5 kA, or is this business of doubling the phase fault current to estimate the short circuit current between all phases a recent thing?
The second problem - is there a reliable means of measuring such low Zes, or is it a fool's errand and you're best just calculating it? From a number of different tests, I'm gaining the impression that the real impedance might be nearer 0.03 R - a small difference, but that would make IPF 50% larger (230/0.03 = 7,666.7 x 2 = 15.3 kA). Even with all best practice my Fluke 1664 reads anything from 0 R to 0.03 R. Note that it's never given a higher reading, which is partly why I think the Ze on the EIC is suspect.
The third problem - I bet you know what I'm about to say! - there're a couple of 400v distribution boards full of 3 pole MCBs with 10kA breaking capacities. Zdb won't be meaningfully greater than Ze at the origin, one is fed off the bus bars, the other from a short run 16mm2 cable (Zdb is still so low I'm struggling to measure it - 0.02 R is commonly returned). Unless I've got something wrong or misunderstood something, the breaking capacity is inadequate - or was is OK to rate them on the single phase fault current 20 years ago? Even if the Ze on the EIC is correct, 2 x 5.75 kA = 11.5 kA.
Thanks.
Obviously this is a three phase supply, so shouldn't they have doubled the PFC and reported it as 11.5 kA, or is this business of doubling the phase fault current to estimate the short circuit current between all phases a recent thing?
The second problem - is there a reliable means of measuring such low Zes, or is it a fool's errand and you're best just calculating it? From a number of different tests, I'm gaining the impression that the real impedance might be nearer 0.03 R - a small difference, but that would make IPF 50% larger (230/0.03 = 7,666.7 x 2 = 15.3 kA). Even with all best practice my Fluke 1664 reads anything from 0 R to 0.03 R. Note that it's never given a higher reading, which is partly why I think the Ze on the EIC is suspect.
The third problem - I bet you know what I'm about to say! - there're a couple of 400v distribution boards full of 3 pole MCBs with 10kA breaking capacities. Zdb won't be meaningfully greater than Ze at the origin, one is fed off the bus bars, the other from a short run 16mm2 cable (Zdb is still so low I'm struggling to measure it - 0.02 R is commonly returned). Unless I've got something wrong or misunderstood something, the breaking capacity is inadequate - or was is OK to rate them on the single phase fault current 20 years ago? Even if the Ze on the EIC is correct, 2 x 5.75 kA = 11.5 kA.
Thanks.