:confused::confused:hi all testing new install warehouse units 2 of first unit Ze 0.09 PSCC 2.45 KA second unit Ze 0.01 pscc off the scale of 20 KA am i too close to sub station help lol
 
Re: Help plz

Hi Mate.

If its a tn-c-s system, ohms law, 230v over 0.09 = 2.5ka, the first unit you tested seems to be ok as long as your mcbs/fuses are rated above 2.45ka. As for the 2nd unit, the ohms law again works out right with your results but that is a high pscc! As I normally only test domestics, I'm not sure how close to a sub station you can be. Although I had a simular problem on a house, the pfc was 9ka and the rcbo's where only 6ka. I rang my boss and he said I must be close to sub station and as long as the main cut out fuse was greater than 9ka then it was ok. The cut out was a bs 1361 type 1 rated at 16.5ka. Not sure if this was ok but the boss says yeah!

Hope this helps abit, although I think I'm just pointing out the obvious.

Cheers

Jay
 
The exemption only applies with a SUPPLY fuse of type BS1361 II 100 Amps max on single phase supply where distribution boards comply with BS60439-3.

In all other scenario's normal rules for device breaking capacities apply.
 
The exemption only applies with a SUPPLY fuse of type BS1361 II 100 Amps max on single phase supply where distribution boards comply with BS60439-3.

In all other scenario's normal rules for device breaking capacities apply.

I'm asking in other scenarios (like this one) when normal rules apply if a BS1361 type II does not have a breaking capacity of 33Ka, like you state what is it rated at?
 
main section board feeding db s has 50 ka rated 3 phase rcd breakers
hopefully this covers all recorded readings on submitted test sheets pointed out to office and approved
thanks all for comments
 
:confused::confused:hi all testing new install warehouse units 2 of first unit Ze 0.09 PSCC 2.45 KA second unit Ze 0.01 pscc off the scale of 20 KA am i too close to sub station help lol

Just a small point, if these are on a 3 phase board you should be recording these figures for your max PFC as either doubled (rule of thumb) or X 1.732

Still within your 50kA max mind :)
 

Reply to low Ze high pscc ???????? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top