Low Zs at socket, Any ideas?? | on ElectriciansForums
Discuss Low Zs at socket, Any ideas?? in the UK Electrical Forum area at ElectriciansForums.net
TheCodboy
Newcastle
Hi all, while testing Zs on a ring final circuit i found one socket to have a particularly low Zs. All others were reading between 0.25- 0.30 but this one was reading 0.08-0.09. Its got a brand new Crabtree double socket installed. A full RFC test has been carried out, and this is the only socket with a reading this low. Obviously i know its better than high, but was just wondering if anyone could shed some light.
Its a TNS system, Ze 0.26
check the leads, batteries and the fuse in back of your mft is nice and tight. then zero/null your leads. retest some of the others to check consistency then re test the problematic one. should give you an indication of whether its the mft or not.
I often find that if i dont use the kewtech kt64dl mft for a few days - say over a bank holiday weekend then on the tuesday the results can be fluctuating a bit, so i now do the things i said above each morning. and my results are now much more stable. i dont seem to get weird anomalies like before.
Its the first time ive used it since its been calibrated, just changed the batteries this morning. Ill try everything again tomorrow!
I had one of those at my last place; it's a really easy tester to use but I found almost bang on the day it was due for calibration I started getting really high readings when I measured Zs using the probes. For some reason it was fine using the plug adaptor, it was just off using the probes. It was fine again after calibration.
operator error. with a Ze of 0.26, it's impossible the get a Ze that low.
Hi - can't have Zs lower than Ze, so likely a measurement error and I'd just redo it :) .
I've always thought that, but what about the following scenarios..
1. Property is TNCS or TNS. The metal pipework on the bonding is deep underground and aids in the Zs (but is not included in the Ze as the main earth has been removed from the MET). If the additional earth pathway created by the bonding outweighs the R1+R2 couldn't the Zs<Ze?
2. Also, what if you have an Ra = 200Ω (TT) and the bonding of the property is also attached to the bonding of the adjacent property which is TNCS? Wouldn't the Zs of the property be influenced by the adjacent properties TNCS?
3. Ra = 200Ω (TT). Pipework on gas/water deep underground. Would this not influence the Zs and perhaps make it <200Ω
Just having a sit in the garden and pondering these deep matters :)
agreed, but why does OP have the low reading at just 1 socket ?
Reply to Low Zs at socket, Any ideas?? in the UK Electrical Forum area at ElectriciansForums.net
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Yes I noticed that too, although the Fluke 1664 that I use claims the same precision (it has a milliohms mode in the high current loop impedance...
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
It is a TNS system, the earth rod is providing an earth reference to make on epile of the supply neutral and is not part of the earth fault loop...
5K
davesparks
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...