S

Spudnik

Afternoon people.

Just finished a PIR on a scout hut with a 3phase 4 wire supply and a very ropey old looking rod buried under the foliage. :D

Thought to my self, "uh-oh"!!

Did a true Ze and got a reading of 0.81 ohms!!!!!!!!!!!

Been racking my brains all day trying to find out why its so low but cant think or find anything.

All circuit Zs would exceptional as well :D


So, what have you had on TT's?
 
sorry mate, thought youmeant that it was un insulated, and ran buried for 40 meters to the rod. I can se what you mean, its one of the old twisted ones that runs through the building to the rod completly uninsulated through out it s length. The only thing I can think of, and I hesitate to say anything to a super moderator, as, factualy i cannot match your experience, ( With supreme respect ) is that I have worked on these, and on their exit throughout the building, they are of course uninsulated but do lay across and make contact with the water pipes etc, I am led to believe that, even if a water supply is not bonded, if a parallel path touches it, it would become an additional earthing rod as its full of water, I would love your coments as still learning and like alll good trademen/craftmen always will be. I can only learn from peeps like you. !
 
The Cu is at high-ish level, out through front of building, round the corner and then clipped along the wall along the soffit, then drops down to the rod.

There are loads of dodgy aspects of the install, well some, and ill post some pics if i go back to do remedials.
 
silly question, but did you disconnect the cable and just test the earth rod?

As it is a 3 phase supply, and the readings are that low, it is very possible that the star point from the transformer neutral has been grounded as well, but as it is TT you still need the earth rods.
 
Last edited by a moderator:

Reply to Lowest Ze on a TT. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top