If the SWA has the additional capacity to cover the bonding as well as serve the earthing requirements of the submain it can be used (unlikely if your equip' bonding is 50mm), if it can't you need to run the full requirements of the earth bonding as an additional cable and not a csa that only makes up the shortfall. Also you can use structural steel as a bonding path and link other services to it as long as it is suitably sized to meet the copper - steel comparison as well as been structurally sound through out its length to your primary structural bonding point from the MET.
 
Last edited by a moderator:
Im not aware why it can't be used if its size and structural integrity are sound then why not? Its a conductive path of suitable low impedance and structurally solid.
 
Steel armour can be used for bonding on tncs but you have to consider the heating effect of diverted neutral currents flowing through the armour as this will affect the cables ccc .
 
Steel armour can be used for bonding on tncs but you have to consider the heating effect of diverted neutral currents flowing through the armour as this will affect the cables ccc .

Can, but will be extremely rare, considering the CSA of the steel armouring needs to be multiplied by 8 X that of copper, ...you'll virtually never see it being used beyond that of a cables CPC...

Why would diverted neutral currents (which will only be seen at time of a fault) flowing in the armouring affect the design CCC of a cable??
 
Last edited by a moderator:

Reply to Main bonding at outbuilding in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
511
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top